Old 07-06-2015, 04:46 PM   #141
Bus Crazy
 
Join Date: Nov 2011
Location: Sault Ste. Marie, Ontario
Posts: 1,223
Year: 1997
Coachwork: Thomas
Chassis: B3800 Short bus
Engine: T444E
Rated Cap: 36
Yeah, I'd say reread the past couple pages of this thread. The subject came up not too long ago. Start on page 10 and read through to the end since some ideas were refined and changed along the way. As mentioned previously, post 130 has an especially nice write-up.
__________________
My build page: Armageddon - The Smell of Airborne Rust
jazty is offline   Reply With Quote
Old 07-06-2015, 04:54 PM   #142
Bus Nut
 
wmkbailey's Avatar
 
Join Date: Jun 2013
Location: Frederick Maryland
Posts: 830
Year: 1999
Coachwork: Thomas
Engine: 3126
Rated Cap: 72
Thanks jazty, I have my bus hooked up this way except my AC ground using shore power. I thought I read that it should be grounded through shore power not to the bus in case of reverse polarity bootleg grounds, else you would have 115 vac on the skin of your bus. I guess if you are always checking you should be good.

I found Mike's first post and you are correct, I need to bond my chassis ground to my AC ground, that way I will be safe. Now I can use the switch that I want.
__________________
William

visvi Cherokee for Journey, Sounds Like Oeesha

http://thejourneyvisvi.com/

My Conversion Thread:
viewtopic.php?f=9&t=464989
wmkbailey is offline   Reply With Quote
Old 07-26-2015, 01:27 PM   #143
Skoolie
 
Join Date: Mar 2015
Posts: 231
I work in the communications industry, we bond every thing.
c_hasbeen is offline   Reply With Quote
Old 07-26-2015, 05:31 PM   #144
Bus Geek
 
Tango's Avatar
 
Join Date: Mar 2011
Location: Houston, Texas
Posts: 4,592
Year: 1946
Coachwork: Chevrolet/Wayne
Chassis: 1- 1/2 ton
Engine: Cummins 4BT
Rated Cap: 15
Electron dimwit here...please explain "bond" idea.
Tango is offline   Reply With Quote
Old 07-27-2015, 12:36 AM   #145
Bus Crazy
 
Join Date: Jan 2008
Location: Upstate NY (Mohawk Valley)
Posts: 1,094
"Bond" is to connect electrically. In a load center, the bus bars may have a long screw that can be inserted to tie the bar to the metal enclosure, or there will be a screw on the enclosure with a metal tab that can be inserted into the buss bar like one of the wires.

Please note that when you are wiring a house, the load center with the main breaker is the main disconnecting means to isolate the house from the utility. The neutral and the safety grounds are always tied together at that location. You can usually see the white wires and the bare wires inserted into the same bus bars.

When you have a sub-panel that is fed off of one of the breakers in the main load center, the neutral should always be insulated from the safety ground. The bare safety ground wires go into one buss bar that is "bonded" to the sub-panel cabinet. The white neutral wires go into a second buss bar that is mounted on insulators. The second buss bar may not come with the load center, it may have to be purchased separately and installed when installing the load center.

Since a bus is not hard-wired to the utility, when on a shore line it is a sub-panel and should have an insulated neutral. The neutral and safety ground can be connected together when isolated from the utility and running on generator. Transfer switches designed for RVs have an extra pole to switch the neutral or ground that is not present in transfer switches made for residential or industrial standby generators.

The bus chassis should be connected to the safety ground but not to the neutral. Whether the shoreline safety ground is bonded to the neutral or not, any campground outlet should be checked for the reverse-polarity bootleg ground before plugging in. If the outlet is reverse polarity, both the neutral and the safety ground will be "hot" compared to the surface under the wheels.

Many people will wire their buses with the neutral and safety ground bonded together like they would when wiring a house with a single load center. It's their bus. This will usually work, but will not work at all if attempting to plug the shoreline into an outlet with ground-fault interruption protection.
__________________
Someone said "Making good decisions comes from experience, experience comes from bad decisions." I say there are three kinds of people: those who learn from their mistakes, those who learn from the mistakes of others, and those who never learn.
Redbear is offline   Reply With Quote
Old 07-27-2015, 11:12 AM   #146
Bus Geek
 
Tango's Avatar
 
Join Date: Mar 2011
Location: Houston, Texas
Posts: 4,592
Year: 1946
Coachwork: Chevrolet/Wayne
Chassis: 1- 1/2 ton
Engine: Cummins 4BT
Rated Cap: 15
Great info...many thanks --- Even if I will have to read it 6 or 8 times. Like I said...electrical dunce...but I gotta' get familiar with this stuff soon.
Tango is offline   Reply With Quote
Old 07-27-2015, 01:36 PM   #147
Bus Nut
 
Join Date: Feb 2012
Location: Salt Lake City Utah
Posts: 958
Year: 2000
Chassis: Blue Bird
Engine: ISC 8.3
Quote:
Originally Posted by c_hasbeen View Post
I work in the communications industry, we bond every thing.
While I agree 100% with Redbear's comment.. when I read this I thought of "bond, noun: a force or feeling that unites people; a common emotion or interest" (Oxford Dictionary). Get it? Communications industry.. supporting emotional bonding.. Maybe it was just an awful pun kind of day for me.
family wagon is offline   Reply With Quote
Old 07-27-2015, 02:02 PM   #148
Mini-Skoolie
 
TheLovelyBus's Avatar
 
Join Date: May 2015
Location: Washington
Posts: 25
Year: 1993
Coachwork: Blue Bird
Chassis: International
Engine: DT466
While it is important to switch both the hot and the neutral when switching between power sources, there shouldn't be any need to switch grounds. You can connect the EGC from the shore power connection, the EGC from the inverter, the EGC going to your bus 120VAC distribution system, and the bus skin connection all together permanently, regardless of your power source.

(EGC = Equipment Ground Conductor = GREEN or BARE COPPER conductor = NOT the WHITE neutral wire.)

(The neutral wire should be bonded to the EGC AT the inverter and NOWHERE else.)
TheLovelyBus is offline   Reply With Quote
Old 07-27-2015, 03:10 PM   #149
Skoolie
 
Join Date: Mar 2015
Posts: 231
Remember how important the electrical system is and how we all just grow accustomed to things being wired correctly and never think of what could happen if an electrical appliance or fixture fails and the easiest path to ground is through a person or pet.

IF an internal components of an appliance, HVAC, power tool, switch, or other electrical equipment has a fault it can energize the metal enclosure and create a touch danger (Line to case failure).
How much voltage does it take to be dangerous?
In a dry environment, 120 Volts through the human body hand to hand or hand to foot the resistance is around 1000 ohms.
What does that actually mean to you and I?
Ohm's law says
I=V/R or 120V/1000 = .120 or 120 mA

120 milli amperes does not sound like very much but it really is lethal.
3 mA = electrical sensation
1 mA = pain with tendency to let go
10 mA = clamp voltage and unable to let go
50 mA for .2 seconds = heart fibrillation or potential death

If you have all of your electrical appliances connected to the same ground reference point then the current from a failure to a low resistant ground and then trip the beaker.(you want to make sure you are not the easiest least resistant path for the current to flow)
lets say your microwave transformer shorted out and was sending current to the metal case, you touch it allow a path to a ground source through your body, either by touching the oven which has a good conductive path to the fuel storage thank which is bolted to the frame and making a great path to return to ground, you are now part of this electrical circuit. Same would be if your plugin in your shore line and something has shorted out and has created the line to case failure and now the body of your bus is hot, you are then part of the circuit.

Most power tools have a three prong power cord to provide an easy path back to trip the breaker by going to ground and not utilizing your body as part of this circuit.
This is why cutting the ground prong off a cord is not a good idea.


Bonding at a communication shelter site is making sure that every conductive piece of material is some how tied to the same ground. This avoids any difference in voltage potential between metal items during a power surge of component failure.

the numbers I used for this are from a training class I have taken, I did not make it up.
thanks
c_hasbeen is offline   Reply With Quote
Old 08-24-2015, 02:36 PM   #150
New Member
 
Join Date: Aug 2015
Posts: 4
Wiring for dummies

[QUOTE=jmsokol;111519]Yes, it is indeed a small world. I started writing my No~Shock~Zone blog because a few of my pro-sound buddies said they had been shocked from their tour bus, and nobody could answer why. I took on the project as an intellectual challenge and found that the majority of electricians and technicians didn't really understand the basic differences between bonding and grounding.

While designing the schematic for a high-current 3-light ground tester I discovered that a bootleg ground condition with the polarity reversed would not be detected by traditional methods, but would still appear to operate normally. However, the entire chassis of the gear would be energized to 120 volts with a low-impedance connection capable of supplying 20 or 30 amps of ground fault current. I named this mis-wired outlet condition an RPBG for Reverse Polarity Bootleg Ground, but had trouble getting the test gear manufacturers to believe that it operated as I described it. They claimed their test gear could discover an RPBG, but after building the test rig as I showed in my demonstration schematic, they all admitted they had never thought about this condition and had not included it in any of their testing or documentation.

I'm seeing the same sort of confusion from the generator manufacturers over the issue of Neutral-Ground bonding and why it's necessary for RV electrical systems, but not for home electrical systems. Seems like a very simple concept to me, which is why I came up with the Neutral-Ground bonding plug as a solution for using a portable inverter generator such as a Honda EU2000i for power their RV. I've had literally hundreds of emails from RV owners who've built and use my G-N bonding plug successfully, but none of these same generator manufacturers want to admit that it works. That's why forums such as this are so important to spreading this basic knowledge. For reference here's the link to my G-N bonding plug article.



Does anyone know of a ground up tutorial on wiring a Skoolie or could mike perhaps provide one. I'm a contractor from ca and know how to wire everything on the inside. What I'm looking for is a precise answer to how do I set up my exterior. I will be running a connection for shore power cut into the side of my bus. I will be setting up a battery bank with bus bars that I want to recharge from shore, alternator, generator, and solar but do not want to draw from the bank while on shore. Also looking at the tesla home battery unit as a bank alternative.
What I don't understand is the order and specificity of the wiring if you have time mike give me a run through from the point of shore connection to the breaker box I'll use inside. How would you do it.
Djavis524 is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bus Electrical Systems - DC Les Lampman Conversion Tutorials and How-to's 64 12-06-2016 10:51 PM
Leveling systems lornaschinske Conversion General Discussions 0 08-04-2012 11:42 AM
Electrical Systems noahyay Conversion General Discussions 11 07-29-2005 06:43 AM
Sewer Systems Steve Conversion Tutorials and How-to's 0 06-16-2004 01:31 PM

» Virginia Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -5. The time now is 08:53 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2016, vBulletin Solutions, Inc.