Electrical code says it's OK...

The quote below is from ~2007 NEC - even though it's "out of date" this isn't the kind of thing that changes drastically, one edition to another, so I'll take it that safety is not the issue with running 120 and 12 V systems in the same conduit:

300.3(C) Conductors of Different Systems.
(1) 600 Volts, Nominal, or Less. Conductors of circuits rated 600 volts, nominal, or less, ac circuits, and dc circuits shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.

Exception: For solar photovoltaic systems in accordance with 690.4(B).

FPN: See 725.55(A) for Class 2 and Class 3 circuit conductors.


Of course, safety and interference are different issues. But since my 12V system only runs a couple small fans and some lights, I'm not really worried about possible interference.
VeldatheWonderbus is offline  
Old 07-18-2016, 06:13 PM   #52
Bus Crazy
 
Join Date: Feb 2012
Location: Salt Lake City Utah
Posts: 1,142
Year: 2000
Chassis: Blue Bird
Engine: ISC 8.3
Ahh, I notice you updated the post to reflect that the root source is NFPA 70 (National Electrical Code) -- IRC and IBC, and maybe UBC also, incorporate NFPA70/NEC by reference. Code is such a mess of reference spaghetti.. It's also really frustrating that one section will indicate that a method is broadly applicable, but another section somewhere else will say "oh by the way.. that one 'applies to everything' requirement actually doesn't apply here."

Such is the situation several of us were thinking of when you cited 300.3(C). Way back in our memories we remembered reading low-voltage stuff wasn't allowed to be commingled with high voltage stuff. I did finally find something along those lines, though actually it's more permissive than I had expected it to be! Class 1 circuits are allowed to be in the same cable, raceway, enclosure, etc with power supply circuits when "the equipment powered is functionally associated." That's in 725.48(B)(1). Class 2 and Class 3 circuits have a whole lot more limitations and it makes my head spin reading them and trying to relate them to something in the real world! The Class 2/3 limitations seem to be along the lines of "don't mix low and high voltage unless it's absolutely required because they both go to the same device/equipment, and then separate them as soon as possible."

That said, I didn't come to recite chapter and verse. I think that if you've colored your wires in such a way that it'll be easy to identify whether a conductor belongs to the 12 or the 120 volt system, and if the insulation on the 12 volt circuits is good for 300+ volts like the stuff on the 120 volt side likely is, then you're probably fine so far as safety is concerned. Not ideal because of the possibility for an inattentive person to cross the 12 and 120 volt circuits despite the wire colors, but good enough for what it is.
family wagon is offline  
Old 07-18-2016, 09:39 PM   #53
Mini-Skoolie
 
Join Date: Jul 2016
Posts: 17
I'm at work right now so I don't really have time to go through and look at all of the posts so I apologize if this is a repeat. My plan at this point is to have everything completely solar power with the option to plug in and also charge my batteries off of the engine if need be. I will have electric appliances ( stove and microwave) my inside and outside lights, and also several plugs that I can plug a TV, xbox, and stuff like that up to. Can anyone give me any advice on how to make this work if it's even possible.

Sent from my SAMSUNG-SM-G891A using Tapatalk
Pudgewomper is offline  
Old 07-18-2016, 11:33 PM   #54
Bus Nut
 
Join Date: Jun 2016
Location: Garden State (rural NJ)
Posts: 383
Heating and cooking with electric requires A LOT of juice.

I'm designing my electrical system for full-time living, over 50% boondocking. I'm cooking and heating with propane. Fridge/freezer, A/C (if/when needed) and other misc will be 120v (from 3000W inverter). All lighting, water pump, etc will be on 12V. 1000W in PV panels and 1000ish Ah in wet cells.

Anything you want is mostly possible. It all comes down to size and money.

Good luck!
BusFiend is offline  
Old 07-21-2016, 06:24 AM   #55
Mini-Skoolie
 
VeldatheWonderbus's Avatar
 
Join Date: Oct 2015
Location: Belgrade, MT
Posts: 65
Year: 1999
Coachwork: AmTran
Chassis: International
Engine: DT466E International
Rated Cap: 72
so many colors! OK, so just four.

Quote:
Originally Posted by family wagon View Post
I think that if you've colored your wires in such a way that it'll be easy to identify whether a conductor belongs to the 12 or the 120 volt system, and if the insulation on the 12 volt circuits is good for 300+ volts like the stuff on the 120 volt side likely is, then you're probably fine so far as safety is concerned. Not ideal because of the possibility for an inattentive person to cross the 12 and 120 volt circuits despite the wire colors, but good enough for what it is.
All of the 12V is blue 12# stranded, insulated for and capable of carrying up to 600V.

All of the 120V uses white, black, and green 12# stranded, also insulated for and capable of carrying up to 600 V.

Cooking will be on the LP range; LP also powers the water heater and refrigerator. We've got a wood stove for heat.

I'll put a big-ass sign in the generator box reminding any user of the color coding
VeldatheWonderbus is offline  
Old 09-27-2016, 02:21 AM   #56
Mini-Skoolie
 
Join Date: Aug 2014
Posts: 38
Quote:
Originally Posted by VeldatheWonderbus View Post
I'm at a standstill on figuring out how to connect my new multi-function stop/turn/driving lights in the rear. Their turn and running light functions work just fine, but I can't figure out how to wire them to get brighter when the brake pedal is depressed. I've gone through the entire buss panel, but none of the connections become energized when the brakes are applied. I'm missing the relevant page (and all the even pages) of the electrical circuit diagram manual (for a DT 466e, if anyone has a copy around, or wants only the odd-numbered pages), so I can't review how the brake lights are connected to the brakes there.

Any advice would be appreciated. Thanks in advance!

(Same question also posted in DT466 forum)

Have you tried the public library I have used the one near me to get wiring schematics for several old trucks . If your not sure ask the reference desk Many times they can get odd weird repair manuals trough the library exchange I have had books from all over the country sent in just be prepared to pay for copies as reference books are normally only allowed to be used in the library and no checking out to take home .

There will probably be a small fee to cover postage and the time frame before having to send it back varies .

__________________
Progress doesn't come from early risers progress is made by lazy men looking for easier ways to do things.
mad_wolf is offline  
Old 12-02-2016, 08:14 AM   #57
Mini-Skoolie
 
Join Date: Apr 2016
Location: New England
Posts: 68
Year: 2003
Coachwork: AmTrans
Chassis: International
Engine: T444E
Battery Charge Rate?

Hi All,

I have a question regarding battery charge rate. I have three VMAX 12v 155 AH Batteries, a 60 amp Renogy Solar Charger, and a 2000w AIMS Inverter with 70 amp Charger.

I ordered the batteries based on AH needed, not realizing that different ones apparently have different specified charging rates? The cut sheet for these batteries says: Charging Current 10A-35A. But then under "Recommended Charging Options" it just says "Smart / Microprocessor controlled charger" and "Charge Controller 25A-UP"

So my question is; Is my Aims Inverter/Charger and/or Solar Charger to powerful for my batteries? Or are the required charging amps cumulative with multiple batteries? Should I get a 4th battery to be safe?

Someone in another post advised that the solar charger side of my system should be fine based on actual wattage coming from my 600W array, but I would assume with the inverter/charger plugged into shore power 70amps will actually be 70amps...

Thanks!!!
WhiteWhale is offline  
Old 12-02-2016, 09:36 AM   #58
Bus Nut
 
AlleyCat67's Avatar
 
Join Date: Oct 2013
Location: Music City USA
Posts: 737
Year: 2005
Coachwork: Thomas
Chassis: Freightliner
Engine: Detroit MBE906
Rated Cap: 72
Others here are more knowledgeable than I, but if memory serves the charge rate you want is 5 to 13% of your total amp hour capacity of your battery bank. 155*3 would be 465 amp hours in total, so your charge current should be between 24 and 60 amps.

4 batteries would bring the amp hours to 620, which would mean a charge current between 31 and 80 amps.

If you can afford to do so I would add the extra battery, not because you particularly need it, but to take full advantage of your charger's output capacity, and also for the extra battery bank capacity. (And also because I prefer an even number of batteries but that's just me.)

Something else you might look at is using 6v golf cart batteries, rather than 12v batteries. My battery bank is going to be a minimum of 12 6v 230ah batteries, connected either 2 in series x 6 in parallel (12v/1380ah) or 4 in series x 3 in parallel (24v/690ah). Total capacity is the same, just different configurations... higher voltage means smaller cables needed to connect everything up. 12v bank with 3000 watt 12v inverter will require 4/0 cables to connect, while 24v bank to 3000 watt 24v inverter can get by with 1/0. And if you step up to 48v 3000 watt inverter 4AWG will be enough. But you'll need to be drawing some serious wattage before you need that.

I'm sure other peeps with more knowledge will chime in.
__________________
My bus - Jasmine - External Build Website - YouTube Channel - TN/KY Meetup Group
As a level 1 burglar, Bilbo got a pony when he accompanied the level 60 dwarves on the Smaug the Dragon raid. Those powerlevelers probably invited him solely so he could trigger fellowship attacks for them.
AlleyCat67 is offline  
Old 12-02-2016, 10:10 AM   #59
Mini-Skoolie
 
Join Date: Apr 2016
Location: New England
Posts: 68
Year: 2003
Coachwork: AmTrans
Chassis: International
Engine: T444E
Thanks AlleyCat!

I am familiar with the concept of charge rate = aprox 10% of amp hour capacity. With that concept alone, I can make my system work! But whats throwing me for a loop is this "10A-25A Charging Rate" listed on the VMAX spec sheet... These two things dont jive!

As for the 6v batteries, I appreciate the insight, but Ive already got quite a wad of cash tied up in these VMAX 12 volts....

Thanks!
WhiteWhale is offline  
Old 12-02-2016, 10:46 AM   #60
Bus Nut
 
AlleyCat67's Avatar
 
Join Date: Oct 2013
Location: Music City USA
Posts: 737
Year: 2005
Coachwork: Thomas
Chassis: Freightliner
Engine: Detroit MBE906
Rated Cap: 72
If you've already got them, may as well use them. For myself though I'd prefer to get more amp hours out of the same size footprint... granted 2 of the GC2 6v are a little larger than a 12v but not enough to really matter. Just keep that on the back burner for when the day comes that you have to replace them.

I would guess that that charge rate shown on the spec sheet is for a single battery... 35A seems high for a 155ah battery... but anyway. Since you are gonna have 3 in parallel, whatever input current you feed them is gonna be split between the 3.

To minimize any difference, connect the positive lead to one end of the string of batteries, and the negative to the other. That way the current has to flow through all 3 to return to the charger.

You might reach out to the manufacturer and see if they can clarify it for you... I'd say your 70 amp charger output will be fine as long as you connect it to all of your batteries, if you use it on just one you'll cook it unless you can reduce the charge current to the appropriate level (or if it is self-regulating, but check with a meter to be sure).
__________________
My bus - Jasmine - External Build Website - YouTube Channel - TN/KY Meetup Group
As a level 1 burglar, Bilbo got a pony when he accompanied the level 60 dwarves on the Smaug the Dragon raid. Those powerlevelers probably invited him solely so he could trigger fellowship attacks for them.
AlleyCat67 is offline  
Closed Thread

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bus Electrical Systems - AC Les Lampman Conversion Tutorials and How-to's 180 12-13-2016 05:50 AM
Leveling systems lornaschinske Conversion General Discussions 0 08-04-2012 10:42 AM
Electrical Systems noahyay Conversion General Discussions 11 07-29-2005 05:43 AM
Sewer Systems Steve Conversion Tutorials and How-to's 0 06-16-2004 12:31 PM

» Virginia Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -5. The time now is 01:21 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.