Solar System / Electrical Diagram Advice

Here is my solar system / electrical plan. I was looking for some feedback. I am by no means an electrician and any help is greatly appreciated.

The Blueprints

segurtj is offline   Reply With Quote
Old 02-14-2018, 02:17 PM   #2
Bus Geek
 
Join Date: May 2016
Location: Eastern WA
Posts: 6,401
Year: 2002
Coachwork: Bluebird
Chassis: All American RE (A3RE)
Engine: Cummins ISC (8.3)
Rated Cap: 72
Looks pretty good to me.

I do see two items right off that cause me question. Perhaps I missed them?

1) I don't see any grounding of the negative side of your inverter. I don't know about Aimes but some do recommend grounding the negative battery to the chassis ground.

2) It looks to me like you have 6 x 12 volt batteries in series. That would yield a 72 volt battery bank.
PNW_Steve is offline   Reply With Quote
Old 02-14-2018, 06:22 PM   #3
New Member
 
Join Date: Jan 2018
Location: Worcester, MA
Posts: 5
So are you saying that 72V of batteries will not be enough?
segurtj is offline   Reply With Quote
Old 02-14-2018, 06:32 PM   #4
Bus Geek
 
Join Date: May 2016
Location: Eastern WA
Posts: 6,401
Year: 2002
Coachwork: Bluebird
Chassis: All American RE (A3RE)
Engine: Cummins ISC (8.3)
Rated Cap: 72
Well....

Finding a charge controller that will work with a 72 volt bank my be challenging as well as finding a 72 volt to 12 volt converter to support your 12 volt loads.

Most of us run 12 volt or 24 volt battery banks along with the odd duck who runs 48 volts.

If you take those 6 x 12 volt batteries and wire them in a series/parallel configuration you can obtain a 24 volt bank. You would connect pairs of 12v batteries in series strings giving you 3 x 24 volt strings. The connect the 3 x 24 volt strings in parallel. This will yield a 24 volt battery bank with 3 times the A/H capacity.

Take a look at this:https://www.batterystuff.com/kb/arti...-tutorial.html it may explain it in a bit more detail.
PNW_Steve is offline   Reply With Quote
Old 02-14-2018, 06:33 PM   #5
Bus Nut
 
Jdawgsfanasty's Avatar
 
Join Date: Dec 2017
Posts: 973
Quote:
Originally Posted by segurtj View Post
So are you saying that 72V of batteries will not be enough?
Not much equipment rated for a 72v input...most equipment is 12vdc or 24vdc...

Sent from my VS500PP using Tapatalk
Jdawgsfanasty is offline   Reply With Quote
Old 02-15-2018, 10:43 AM   #6
Bus Crazy
 
JDOnTheGo's Avatar
 
Join Date: Feb 2017
Location: The West
Posts: 1,210
Year: 1998
Coachwork: MCI
Chassis: 102 EL3
Engine: DD 60
In addition to what the others have said, I'm not sure about connecting the shore/generator transfer switch output and also the inverter output to the 120VAC panel. I guess there is no reason not to do this as long as you are sure you have only one of those three sources providing power?? I'm not sure. Maybe the reason is that the shore or generator "input" would be hot as shown (when the inverter is operating).

I put another transfer switch in my system at that point.
__________________
JD - Full timer out west
Missy - 1998 MCI 102-EL3 - 1.7kW Solar - 10kWh Lithium
My Adventures & Build
JDOnTheGo is offline   Reply With Quote
Old 02-15-2018, 11:11 AM   #7
Bus Geek
 
Join Date: May 2016
Location: Eastern WA
Posts: 6,401
Year: 2002
Coachwork: Bluebird
Chassis: All American RE (A3RE)
Engine: Cummins ISC (8.3)
Rated Cap: 72
Quote:
Originally Posted by JDOnTheGo View Post
In addition to what the others have said, I'm not sure about connecting the shore/generator transfer switch output and also the inverter output to the 120VAC panel. I guess there is no reason not to do this as long as you are sure you have only one of those three sources providing power?? I'm not sure. Maybe the reason is that the shore or generator "input" would be hot as shown (when the inverter is operating).

I put another transfer switch in my system at that point.
I think that the Aimes inverter that he is looking at has a built in transfer switch.
PNW_Steve is offline   Reply With Quote
Old 02-15-2018, 12:02 PM   #8
Bus Crazy
 
roach711's Avatar
 
Join Date: May 2010
Location: Farmington Hills, Mi (Detroit area)
Posts: 1,968
Year: 2000
Coachwork: Eldorado Aerotech 24'
Chassis: Ford E-450 Cutaway Bus
Engine: 7.3L Powerstroke
Rated Cap: 19
I'm guessing that you want a 12 volt system. In that case you would change the yellow jumpers between the individual batteries. Instead of a jumper connecting the positive on one battery to the negative of the next (which will give you a 72 volt system), you would jump from positive to positive and negative to negative for a 12 volt system.

12 volt parallel connections (pos to pos and neg to neg) add the battery amps while leaving the voltage the same. For example, assuming your batteries are rated at 225 amps, your system would be 12 volts and 1350 amps.

Now, take the same 6 batteries and connect them in series (pos to neg) and you now have a 72 volt system with 225 amp capacity.

Parallel cabling adds the amps and series cabling adds the volts.
__________________
The Roach Motel
roach711 is offline   Reply With Quote
Old 02-15-2018, 12:08 PM   #9
New Member
 
Join Date: Jan 2018
Location: Worcester, MA
Posts: 5
Thanks everyone for the help!! I changed the battery connections so now it is a 12v system. I also ran the shore/generator power straight to the inverter which has a built in auto relay. Am I correct in grounding the Inverter and both panels to the chassis? Anything else I might be missing?

UPDATED: The Blueprints
segurtj is offline   Reply With Quote
Old 02-15-2018, 01:38 PM   #10
Bus Geek
 
Join Date: May 2016
Location: Eastern WA
Posts: 6,401
Year: 2002
Coachwork: Bluebird
Chassis: All American RE (A3RE)
Engine: Cummins ISC (8.3)
Rated Cap: 72
My installation on my last bus more closely followed your first transfer switch configuration.

That gave me the ability to "automatically" disconnect high current loads when I was running on invert power.

Not sure if I can describe this properly,.....

I ran shore and generator into the transfer switch. The load side of the transfer switch went to the load center mains. Then I wired branch circuits for all of the high current loads and one branch circuit to the inverter input (ATS built in) and the inverter output went to a sub panel for connection to inverter powered branch circuits.

In use, it auto switched between generator and shore power. When one of those two was available then all branch circuits are powered from shore/generator. In the absence of shore/generator power the ATS in the inverter will power up the inverter backed circuits and the non-inverter backed circuits are dead.

I hope that makes sense
PNW_Steve is offline   Reply With Quote
Reply

Tags
diagram, electrical, solar, solar system


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -5. The time now is 07:34 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.