Electrical calculations

So I crunched numbers tonight for fridge, microwave,coffee maker, lites, exhaust fan,water pumps, etc based on average use during 24 hr period and came up 167.2AH load. This including a 80% efficiency to be safe . My stove , water heater , and space heater will be on propane. Will a 200AH battery bank suffice or should I go with 300AH to add as a buffer. What are your thoughts. Thanks again.Also using 3KW inverter for fridge, microwave, coffee maker, and a few minor outlets.

Mat7783 is offline   Reply With Quote
Old 01-14-2020, 06:33 AM   #2
Bus Crazy
 
Ronnie's Avatar
 
Join Date: Oct 2017
Location: Virginia
Posts: 2,325
Year: 1971
Coachwork: Wayne
Chassis: International Loadstar 1700
Engine: 345 international V-8
Generally speaking you do not want to use more then half your batteries capacity. So double the 167ah figure. Then that only gets you one day. Not sure how you plan to charge your batteries, but if by solar then you would be assuming all sunny days.
Ronnie is offline   Reply With Quote
Old 01-14-2020, 07:42 AM   #3
Skoolie
 
matthews2001's Avatar
 
Join Date: Oct 2018
Location: Southern VT
Posts: 154
Year: 2001
Coachwork: Thomas Bus
Chassis: Allison MD 3060
Engine: Catepillar 3126B 210hp/605 ft lb
look at thread:

Voltage drop using inverter (Multi-page thread 1 2)
matthews2001 (couldnt figure out how to post link to thread)


maximum inverter size really looks like 1000 watts, bigger one will decrease battery life
matthews2001 is offline   Reply With Quote
Old 01-14-2020, 07:45 AM   #4
Skoolie
 
Join Date: Dec 2019
Location: Sanford Florida
Posts: 200
Year: 2000
Coachwork: Thomas
Chassis: MVP/ER
Engine: Cat3126B 230hp
Rated Cap: 48
I plan to use inverter generator with 8,3amp 12v outlet or RV site power thru generator fir recharging of batteries.
Mat7783 is offline   Reply With Quote
Old 01-14-2020, 07:49 AM   #5
Skoolie
 
Join Date: Dec 2019
Location: Sanford Florida
Posts: 200
Year: 2000
Coachwork: Thomas
Chassis: MVP/ER
Engine: Cat3126B 230hp
Rated Cap: 48
What about the startup wattage and amperage of a microwave and coffee maker and hair dryer. Wouldn’t any combination of these appliances run over 1kWatts?
Mat7783 is offline   Reply With Quote
Old 01-14-2020, 07:57 AM   #6
Skoolie
 
matthews2001's Avatar
 
Join Date: Oct 2018
Location: Southern VT
Posts: 154
Year: 2001
Coachwork: Thomas Bus
Chassis: Allison MD 3060
Engine: Catepillar 3126B 210hp/605 ft lb
I think thats the point. Microwaves and hair dryers are really too many watts to use from normal rv/bus 12v setups for battery life and draw. This assumes 4 6 volt t-105 trojan deep cycle batts, about $800, a typical setup.

It will "work" but at great cost to batteries
matthews2001 is offline   Reply With Quote
Old 01-14-2020, 08:38 AM   #7
Bus Crazy
 
TheHubbardBus's Avatar
 
Join Date: Apr 2019
Location: SW USA
Posts: 2,064
Year: 2003
Coachwork: IC / Amtran
Chassis: CE300
Engine: International T444e
Rated Cap: 23
Quote:
Originally Posted by Mat7783 View Post
So I crunched numbers tonight for fridge, microwave,coffee maker, lites, exhaust fan,water pumps, etc based on average use during 24 hr period and came up 167.2AH load. This including a 80% efficiency to be safe . My stove , water heater , and space heater will be on propane. Will a 200AH battery bank suffice or should I go with 300AH to add as a buffer. What are your thoughts. Thanks again.Also using 3KW inverter for fridge, microwave, coffee maker, and a few minor outlets.

First off, battery chemistry matters. For deep cycle LA chemistries (including FLA & AGM) you have ~50% usable capacity. And cycle life will improve the less of that you use. So best case (or worst case, for your batteries), 200AH is 100AH. With Lithium, you've got ~80%.


Also, you have to consider how much you're pulling at any one time. The AH rating is usually based on a C/20 discharge rate. So for 200AH, that's 10A continuous. Any higher discharge & you're going to see less in actual capacity. Also, high discharge rates - particularly w/ LA - will lead to shorter battery life.


I'm assuming this is a solar system. If so, you'll have to consider sizing the panels so that you'll be able to restore the AH used during the course of the day. You'll also need to determine how many days of no-sun autonomy you're comfortable with. For instance, you've got one day planned for above (before considering the other factors mentioned). If it's a cloudy day, you may not get all that back. If it's a rainy day you may not get any back. So in one day, you could be done. If you're ok w/ that (generator power, etc), then no problemo. Otherwise, your AH capacity needs to double for each day you need storage for.


Finally, don't forget to add in the amount of juice your inverter is using, both in the process of inverting, as well as in standby. These numbers, particularly the former, can be considerable. Your inverter will basically be sized by your anticipated peak loads... the max amps you plan on pulling at any one time. Best bet is to try to tailor your inverter size so it meets this amount, with little excess, as the larger the inverter, the more power it draws.


EDIT. Just saw the bit about planning to use a generator. Sorry. Feel free to discount all the solar stuff then ;) Everything else applies however.
__________________
Go away. 'Baitin.

Our Build: Mr. Beefy
TheHubbardBus is offline   Reply With Quote
Old 01-14-2020, 09:59 AM   #8
Skoolie
 
Join Date: Dec 2019
Location: Sanford Florida
Posts: 200
Year: 2000
Coachwork: Thomas
Chassis: MVP/ER
Engine: Cat3126B 230hp
Rated Cap: 48
Thanks for all the info.
Mat7783 is offline   Reply With Quote
Old 01-14-2020, 10:54 AM   #9
Bus Geek
 
Join Date: Nov 2016
Posts: 2,775
A 3000W or 5000W inverter is not the issue, so long as the bank and daily energy inputs support them properly.

Obviously costs and weighs a lot more than one stressed by 1000W.

And if the gennie is supporting running the big loads, then even the small bank will be fine.

Make up a detailed energy budget, figure out your Ah per day needs, where the inputs for 115% of that are coming from, and design the system to support those numbers.
john61ct is offline   Reply With Quote
Old 01-14-2020, 02:17 PM   #10
Bus Nut
 
Join Date: Apr 2019
Location: Savannah GA
Posts: 756
Year: 2003
Coachwork: Bluebird
Chassis: TC2000
Engine: Cummins 5.9 24v
Rated Cap: 54 passenger
Quote:
Originally Posted by TheHubbardBus View Post
First off, battery chemistry matters. For deep cycle LA chemistries (including FLA & AGM) you have ~50% usable capacity. And cycle life will improve the less of that you use. So best case (or worst case, for your batteries), 200AH is 100AH. With Lithium, you've got ~80%.


Also, you have to consider how much you're pulling at any one time. The AH rating is usually based on a C/20 discharge rate. So for 200AH, that's 10A continuous. Any higher discharge & you're going to see less in actual capacity. Also, high discharge rates - particularly w/ LA - will lead to shorter battery life.


I'm assuming this is a solar system. If so, you'll have to consider sizing the panels so that you'll be able to restore the AH used during the course of the day. You'll also need to determine how many days of no-sun autonomy you're comfortable with. For instance, you've got one day planned for above (before considering the other factors mentioned). If it's a cloudy day, you may not get all that back. If it's a rainy day you may not get any back. So in one day, you could be done. If you're ok w/ that (generator power, etc), then no problemo. Otherwise, your AH capacity needs to double for each day you need storage for.


Finally, don't forget to add in the amount of juice your inverter is using, both in the process of inverting, as well as in standby. These numbers, particularly the former, can be considerable. Your inverter will basically be sized by your anticipated peak loads... the max amps you plan on pulling at any one time. Best bet is to try to tailor your inverter size so it meets this amount, with little excess, as the larger the inverter, the more power it draws.


EDIT. Just saw the bit about planning to use a generator. Sorry. Feel free to discount all the solar stuff then ;) Everything else applies however.
Not OP but it helps me. I want to get as dependent on solar as I can. And even if I read it 15 times today, if I could be the 16th time it finally makes sense in my head LOL. So thanks for typing it out.
JDSquared is offline   Reply With Quote
Old 01-14-2020, 03:11 PM   #11
Bus Crazy
 
TheHubbardBus's Avatar
 
Join Date: Apr 2019
Location: SW USA
Posts: 2,064
Year: 2003
Coachwork: IC / Amtran
Chassis: CE300
Engine: International T444e
Rated Cap: 23
Quote:
Originally Posted by JDSquared View Post
Not OP but it helps me. I want to get as dependent on solar as I can. And even if I read it 15 times today, if I could be the 16th time it finally makes sense in my head LOL. So thanks for typing it out.

I am extremely pleased you found it helpful
__________________
Go away. 'Baitin.

Our Build: Mr. Beefy
TheHubbardBus is offline   Reply With Quote
Old 01-14-2020, 03:45 PM   #12
Skoolie
 
bubb, the real one's Avatar
 
Join Date: Dec 2014
Location: central texas
Posts: 170
Year: 1990
Coachwork: Thomas/International
Chassis: 3700
Engine: 7.3
Rated Cap: 72
Amps

Is that number in ac amps or dc amps,
bubb, the real one is offline   Reply With Quote
Old 01-22-2020, 07:44 AM   #13
Skoolie
 
Join Date: Jul 2019
Posts: 119
Year: 2002
Chassis: Van
Engine: 5.7L Gas
Quote:
Originally Posted by matthews2001 View Post
look at thread:

Voltage drop using inverter (Multi-page thread 1 2)
matthews2001 (couldnt figure out how to post link to thread)


maximum inverter size really looks like 1000 watts, bigger one will decrease battery life

So I'm trying to figure out this whole inverter thing and I feel like I keep seeing different opinions. I realize that the process of inverting to 120V is (I believe) around 80 percent efficient. But you are saying that a bigger inverter is less efficient so I should go with as small of an inverter as possible? Originally I was planning on going with a slightly bigger inverter then what I needed just to make sure it would cover everything I needed.
mitchk is offline   Reply With Quote
Old 01-22-2020, 07:57 AM   #14
Bus Geek
 
Join Date: Nov 2016
Posts: 2,775
Good efficiency comes from servicing a load that is close to the inverter's actual maximum continuous capacity.

So a 2000W inverter powering a 150W load will be very inefficient.

The other factor is only turning the inverter on when it is needed.

https://sprinter-source.com/forum/sh...d.php?p=842667
john61ct is offline   Reply With Quote
Old 01-22-2020, 08:15 AM   #15
Skoolie
 
Join Date: Jul 2019
Posts: 119
Year: 2002
Chassis: Van
Engine: 5.7L Gas
Quote:
Originally Posted by john61ct View Post
Good efficiency comes from servicing a load that is close to the inverter's actual maximum continuous capacity.

So a 2000W inverter powering a 150W load will be very inefficient.

The other factor is only turning the inverter on when it is needed.

https://sprinter-source.com/forum/sh...d.php?p=842667
This helps a lot. Thanks! I will probably try to go with a 1000W inverter. If I need to go a little bit bigger it probably isn't a big deal as long as I turn off the inverter whenever I am not using it.
mitchk is offline   Reply With Quote
Old 01-22-2020, 11:49 AM   #16
Bus Nut
 
Join Date: Dec 2018
Location: Mt Vernon, WA
Posts: 523
Year: 1996
Coachwork: Bluebird, Collins
Chassis: G30 Bluebird Microbird, E350 Shuttle Bus
Engine: 1995 Chevrolet 350, 1992 Ford 460
I’ll be going with a combination medium sized 2500 watt inverter charger and a small 600 watt inverter. The big inverter is 92% efficient but will be in Search mode most of the time.
Doktari is offline   Reply With Quote
Old 01-22-2020, 03:41 PM   #17
Skoolie
 
bubb, the real one's Avatar
 
Join Date: Dec 2014
Location: central texas
Posts: 170
Year: 1990
Coachwork: Thomas/International
Chassis: 3700
Engine: 7.3
Rated Cap: 72
AC-dc

167 amps calculated draw, is this AC amps or DC amps
bubb, the real one is offline   Reply With Quote
Old 01-22-2020, 04:03 PM   #18
Bus Nut
 
Join Date: Dec 2018
Location: Mt Vernon, WA
Posts: 523
Year: 1996
Coachwork: Bluebird, Collins
Chassis: G30 Bluebird Microbird, E350 Shuttle Bus
Engine: 1995 Chevrolet 350, 1992 Ford 460
that 167 amps would have to be DC. AC would be 20,040 watts at 120 VAC. 167 amps at 12 volts about 2338 watts at 14 volts.
Doktari is offline   Reply With Quote
Old 01-22-2020, 06:56 PM   #19
Skoolie
 
Join Date: Dec 2019
Location: Sanford Florida
Posts: 200
Year: 2000
Coachwork: Thomas
Chassis: MVP/ER
Engine: Cat3126B 230hp
Rated Cap: 48
That’s 167ah load on DC 12V. Battery. Will use inverter to power 10cu’ fridge and 700w microwave 5 minutes daily, hair dryer on low setting, coffee maker in morning etc. fridge is only constant draw of ac voltage. Everything else is 12VDC such as lighting, fans, water pumps etc. size of inverter is the puzzle and battery bank size??
Mat7783 is offline   Reply With Quote
Old 01-23-2020, 04:59 AM   #20
Bus Crazy
 
JDOnTheGo's Avatar
 
Join Date: Feb 2017
Location: The West
Posts: 1,210
Year: 1998
Coachwork: MCI
Chassis: 102 EL3
Engine: DD 60
Quote:
Originally Posted by Mat7783 View Post
...size of inverter is the puzzle and battery bank size??
I think you are asking your question again. If that is not the case, ignore the following, I'm mostly just repeating what has already been said.

1. Assume your daily power consumption estimate is low and/or batteries are less than 'brand new' - round up to 200Ah/day. (plus it makes the math easier )

2. Assuming lead-acid batteries, you need a 400Ah bank to provide 200Ah/day (more complicated than that but good enough for now). How many days do you want to be able to operate this setup from battery bank alone? Three?? You need a 1200Ah bank (to provide 600Ah over three days).

3. Determine your maximum AC power requirement (everything running at the same time) being aware of start up current and pick an inverter to provide that.

Sadly, there are very few easy answers - there are many "it depends." All of the above can be picked apart and reasons found to make it inaccurate.

... and, include a 'better' battery monitor in your system so you can take reasonable care of that battery bank.
__________________
JD - Full timer out west
Missy - 1998 MCI 102-EL3 - 1.7kW Solar - 10kWh Lithium
My Adventures & Build
JDOnTheGo is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -5. The time now is 06:50 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.