01-21-2017, 02:02 PM
Year: 1987
Engine: 6.9L Diesel
I hope you take lots of pictures for your setup and report back here! I'm also interested in using the renogys so I'd love to hear your review.
I do not have my solar setup done yet, I am not an electrician. Opinion of a amateur below.
You may be fine with 10 gauge but I would advise against it. Assuming you have 600 watts of solar panels, at 12v you'll have 50 amps of current to transfer (I know that it will be charging at 18v and you likely won't have a full 600 watts coming in at once). However from my amateur engineering standpoint I think it is wise to plan around max amperage(if not more) regardless.
According to this wire gauge chart you best use 8 gauge wire to transfer 50-65 amps for a 7-10 foot run. I personally plan on using 4 gauge, because I am a fool who is all about overkill (and I impulse bought 50 feet awhile ago). Considering you have more than 1k put into your setup, it makes sense to dump some relatively modest money into some nice thick wire to make sure you have more than enough copper to carry your solar amperage to your batteries.
I plan on using 00 wire between my batteries(because I also have 50 feet laying around), and using 4 gauge between my batteries and invernter charger (8 gauge should be plenty fine here, but I have lots of 4 gauge).
From shore to inverter, I would follow the chart and overkill a bit. My shore to inverter will probably be about 20 feet so I will try to do atleast 8 gauge.
I'm assuming you've visted handybob's website, and have a trimetric(or other) battery monitor, but if you haven't you definitely should. https://handybobsolar.wordpress.com/...ging-puzzle-2/
He agrees with most of the equipment you're using though, right on!
Good luck and come back with reports and pictures! LOTS of pictures! and details, and PICTURES!
edit: and make sure you charge your batteries at the correct voltage specified on the manufactures website. (14.8v I think for crown)
01-21-2017, 02:04 PM
you would think Renogy would specify.
here is the table that i used.
http://assets.bluesea.com/files/reso...on_chartlg.jpg
01-21-2017, 04:03 PM
I agree totally here, bigger is best. The only problem with that is finding all the lugs to make the connections fit. Takes a bit of improvising, but buy big copper as suggested to reduce resistance in any circuit.
Connection lugs can sometimes be adapted and drilled out to fit whatever bolts you encounter but make sure they are rated for at least the amperage carried by the wire/cable.
01-21-2017, 07:51 PM
Hi,
I also went with Renogy and am very delighted with thier products.
As for wire gauge, i half wonder if when i add more panels to mine if i might just designate half the panels, batteries, and a separate charge controller to the shop area. I'm never going to use more than 2k watts in the shop. This way i can keep from needing gigantic wires from the batteries. Split the system up into two. Hmm...
Excited to see what you decide. Good luck!
01-21-2017, 11:08 PM
Engine: TE 444
Rated Cap: 12
600 watts at 12 volts is 50 amps, you need 8 gauge wire at minimum, 6 gauge would be better, the 30 amp shore power cable can be 10 gauge
01-22-2017, 02:04 AM
Your wires to your inverter need to be at least 2ga and really should be 0ga. 1500W at 12V is 125A, that's solidly in 0ga realm.
01-22-2017, 01:53 PM
The spec sheet indicates each panel will be putting out no more than 5.25 optimum amperage and 5.75 short circuit amperage. I should be under 36 amps total in full sun, no? Not to be argumentative but I think I'm pumping out closer to 400 watts / sun hour if I adjust for efficiency (generally ~66%) and with that correction I'm at 33 amps in full sun, closer to the manufacturer specifications.
If I am correct in understanding this, 600 watts at 12v isn't putting out 50 amps, but roughly 30% less than that. And reading the chart, from 20 amps all the way up to 50 amps I should be safe with 10ga.
I'm most concerned with the gauge I'm going to use between all the batteries wiring them in series/parallel. How do I calculate the proper amp draw on that? I see a lot of people using 00 (aka 2/0) and will probably go with that. I can get 10 feet for 50 dollars or so and that might cover all of my cable runs except shore power.
And what about from the batteries to the charge controller?
01-22-2017, 08:18 PM
Coachwork: Tomas
Engine: T444e
Rated Cap: 54
This should answer most of your questions.....
1) Solar panels to charger controller you need 8 gauge wire.
Solar panels will charger at around 18 volts, so it is less amps. You are correct in your 35 amp figure.
2) what ever you used from the solar panels to the charge controller is what you use on the battery side.
3) with a 1500 watt inverter, you will be drawing around 150 amps, so 2 gauge welding cable is plenty (rated at 200 amps at up to 50 feet)
4) use what ever you use to connect the inverter to the batteries to interconnect the batteries.
5) for shore cable run what ever it will be fused at... 15 amps=14ga. 30 amps=10ga.
I have a small solar setup on my house, I run 20 amps worth of panels through 75 feet of 10 gauge and then 30 feet of 8 gauge. My 1000 watt inverter is wired with 4 gauge welding cable.
The most important factor is the quality of the wire. I use welding cable over automotive battery cable as the insulation is more robust and has a higher temperature rating.
Most of my extension cords are home made out of sjoow wire, have you ever tried to run 15 amps on a 100 foot 14 gauge cord? It will trip the breaker, Mine will not.
As long as you use high quality wire, what I have listed will be fine.
Overkill is a waste of time and money if high quality components are used.
"...Baler twine tie downs goin' down the road
On two bald tires and an oversize load..."
01-22-2017, 08:51 PM
TAOLIK, thank you for your response. I had actually been in communication with Handy Bob a few months ago and realized I should have just contacted him again. I'll get his opinion on everything and post it so that anyone designing a similar system can get their own HandyBob approved setup ;)
Hank, thank you for your advice. This helps me HUGELY. I had purchased some 2/0ga wire for ~$2.50/ft on Amazon (welders cable) awhile ago for a separate project.. With $30 worth of cable/lugs I should be able to hook up all my batteries and inverter. I upgraded on your recommendation on 8ga from the panels to charger to batteries and opted for 6ga as my inverter calls for a 6ga ground anyway. How do I hook up 6ga wire with an MC4 connector though? I can't find any MC4 cable in anything bigger than 10ga... =| It was only marginally more expensive at ~$1/ft.
Bob did tell me I might have an issue using the inverter I purchased as it doesn't have internal ground and neutral bonding. I'll update about that after I call him tomorrow.
Thanks again, you have all been very helpful.
01-22-2017, 09:57 PM
Coachwork: Tomas
Engine: T444e
Rated Cap: 54
You do not want your ground to be nutral bonded in a bus. This is for several reasons.
1) The shore supply will be bonded and it is extremely dangerous to have nutral bonded twice as it causes a "ground loop".
Current will be able to flow through both nutral and ground, so ground won't be "free" in an emergency.
2) the whole bus body is metal, so if anything is wired backward you will electrify the bus body.
Say whoever installed the shore power outlet at the campground switched the hot and nutral, the hot wire would be connected to your nutral and ground. This could kill you if you touch the bus and earth at the same time, unless the campground supply is properly grounded.
That is a big risk to take, to assume any one has done anything right before you is what kills.
