Old 10-04-2016, 11:57 PM   #21
AlleyCat67's Avatar
Year: 2005
Engine: Detroit MBE906
Maybe I'll give this one a go.... a few bucks more but it's a name I know.
Briggs and Stratton 2000 Watt Generator
Old 11-29-2016, 11:06 AM   #22
Coachwork: AmTrans
Originally Posted by Iceni John View Post
A 60A MPPT charge controller can provide a maximum of 60A into the batteries, regardless of battery system voltage. If you have a 12V battery system it can provide about 888W (60A x 14.8V); if you have a 24V battery system it can provide twice that wattage at the same 60A maximum current.
A 600W PV system will not usually produce 600W of electrical power - it will typically produce a maximum of about 3/4 of that under most conditions, i.e. you will see about 450W from the panels most days. 450W divided by 14.8V battery charging Absorb voltage (needed for Trojan T-105 batteries in a 12V system) is about 30A, less the CC's own inefficiencies that will drop its output to just under 30A. In other words, your 60A CC is able to be powered from a lot more than 600W of panels. I have two Morningstar TS-MPPT-60 CCs that are each fed by 1020W of panels, and each CC charges four golfcart batteries in series/parallel at about the maximum recommended charge rate 0f 13%. FLA deep-cycle batteries should ideally be charged at between 5 to 13% of their 20-hour Ah rating.
Don't forget to keep all your DC cables short and fat to minimize voltage loss under load. If you need further good advice, it's worth your while to read the Northern Arizona Wind & Sun forum - there's enough expertise and experience there to answer any questions you may ever have.
I have a second phase of the same question. The 2000 watt AIMS inverter/charger I purchased ( 2000 Watt Pure Sine Inverter Charger ) says is puts out a charge rate of 70 amps. The VMAX 155AH batteries I purchased ( https://www.vmaxtanks.com/SLR155-AGM...ery-_p_66.html ) say they have charging current of 10-35 amps. Is this a problem? Does the number of batteries effect this at all? I currently have 3 of them.
Thanks!
WhiteWhale is offline   Reply With Quote
Old 11-29-2016, 05:50 PM   #23
Blkjacksabbath's Avatar
Check out a post I saw on Reddit. Not directly solar related, but any power reducing hacks may help with a solar-battery setup.
"First one that has actually helped in several ways: If you have an add-on TV that you need an inverter for, check the plug. A lot of the generic TVs actually just take the 120V in the power brick and convert it back into 12V power. By wiring directly into a 12V plug I bought from radio shack, I was able to power my TV directly from DC, saving an ugly inverter's noise and overhead. I also believe (though I didn't measure it) that the TV even uses less power than it did before, though it could just be that I had a really inefficient inverter."
https://www.reddit.com/r/GoRVing/com...best_rv_hacks/
Blkjacksabbath is offline   Reply With Quote
Old 12-09-2016, 12:10 PM   #24
Coachwork: AmTrans
How do I regulate between solar charger and Inverter/Charger? Do I need to put in a switch to isolate so that both arent charging batteries at the same time? I guess it would be easy enough to shut off solar when using inverter charger but I wouldnt really ever want to shut off the inverter charger side considering it also is providing the 12v power source to the inverter to go to AC....
Old 12-09-2016, 12:30 PM   #25
AlleyCat67's Avatar
Year: 2005
The way you'll want to set it up is have the AC from shore or generator feeding thru a breaker in your main load center to the AC IN connection on the inverter/charger, with the AC OUT wired to a transfer switch with the other side of the switch connected to another breaker in the main load center, and the output of the transfer switch feeding a subpanel which will power your inverter loads. The transfer switch will feed the subpanel with shore or generator when available, and only pull from inverter when necessary.
All shutting the charger side of it down does is stop the charge function. As long as the inverter is switched on it will produce 120VAC power as needed, up to the power limit of whatever model you're using. When you're connected to shore power the charge side will keep the batteries topped off so there wouldn't be any need to charge from the panels, though of course there's nothing that says you can't keep the charger side turned off and continue charging from solar.
Old 12-14-2016, 09:27 AM   #26
Coachwork: AmTrans
What you are saying makes sense, but I am still not sure how I would/should protect my solar/charge controller from the charge output coming from the inverter when using the inverter to charge the batteries.?
Old 12-14-2016, 10:49 AM   #27
AlleyCat67's Avatar
Year: 2005
You have a couple of options..... the simplest is to find a transfer switch rated for the voltage and amperage of the higher charge current (solar or inverter).... wire the solar charge controller to the NC contacts and the inverter to the NO contacts. This way the solar charge controller is connected to the batteries until the inverter charger is activated, then the transfer switch cuts over to that, electrically isolating the solar controller from the battery bank.
You could also find a charge controller that will handle multiple inputs and connect both solar panels and inverter charger output to it, and let it regulate charge current, or use multiple charge controllers that will talk to one another (they are available but costly).
Another choice, though somewhat less desirable, is to connect some large diodes between the solar controller and the batteries. In case you don't know, a diode is like a one-way valve for DC current. The diods will allow the current FROM the solar controller to get to the batteries but current coming from the inverter will not be able to pass.
Old 12-14-2016, 11:23 AM   #28
Chassis: B3800 Short bus
There shouldn't be any reason to disconnect one while the other is working. Both the solar charge controllers sense voltage for operation and have internal diodes. While one is working the other will sense the voltage and turn off or down.
In essence, connect both to charge controllers directly to the batteries and you'll be fine
Old 12-14-2016, 02:28 PM   #29
Coachwork: AmTrans
Ok. That seems like what most systems looked like to me but I wasn't sure if I was missing something and the last thing I want to do is fry an expensive piece of equipment. And a transfer switch I don't think would really work because Id have to choose between solar charging and using my inverter, but not both at the same time.
My next question is how to fuse the inverter/charger and solar charger circuits individually. The 60 amp solar charge controller came with a 60 amp inline fuse, but the inverter/charger is 70 amp and uses different size wire and fuse. Will the higher charging output from the 70 amp inverter/charger be an issue for the connected 60amp solar circuit?
Old 12-14-2016, 04:44 PM   #30
If the solar charge controller requires a 60 amp fuse, then put that fuse between the batteries and solar charge controller. If the inverter/charger requires a 70 amp fuse, then put that fuse between the batteries and inverter/charger. That's all there is to it. One doesn't affect the other.