So I would run the 3 lefts in series and the 3 rights in series and parallel the 2 runs, or vice versa?
|
According to the spec sheet you cannot exceed 60 amps or it will trigger the short circuit switch in the controller.
if each side is 36v at 8.3 amps and you wire them in parallel to the controller you have 16.6 amps in and when it's converted to 12 is about 50 amps which is in spec but on the high end of the rating.
So yes the two strings of 3 in series wired in parallel to the controller should be ok.