Old 03-20-2019, 10:02 AM   #1
Red face Switches and Grounding Questions
Let me start by saying that I have been reading ALOT on this forum about electrical and have come to learn that being an electrician is not anywhere in my future
I have scoured this thread, as well as this one, been reading here and a few other places.
I have purchased the majority of what I need for my electrical system. The solar panels are mounted on the roof. The inverter and charge controller are sitting in the opened box ready to be installed. I have 5 feet of red and black 4/0 gauge wire as well as some 10, 6, and 8 gauge wire for other parts of the system. I have all of the wires ran for appliances and outlets as well. I have built an airtight battery box for my flooded lead acid batteries that vent to the outside of the bus. Now comes the scary part. Making it live
Here is a diagram of my plan to set up everything. Please note the connectioin of the DC and AC circuits to the batteries is a little screwy because of the website I was using
Here are where my questions come in. I know that my inverter has a ground-neutral bond internally. I know that under no circumstances can the inverter and shore power be grounded at the same time( right?!?!).
The inverter has a grounding lug that I was going to attach to an installed bus bar on the chair rail. The shore power plug also needs to be grounded. Can I ground them to the same bus bar and use my master switch to cause a break in the circuit between the inverter and the AC distribution panel to remove the double ground? If not how should I approach the need of both the inverter and the shore power plug both needing to be grounded?
Next question, I have an extra grounding bar. Is there a need of one in the DC circuit?
I feel like i am missing a fuse somewhere. Possibly between the charge controller and the batteries?
Do the batteries need to be grounded as well?
I know that this is alot of questions and some of them maybe stupid, but I know that I am no where close to being an expert in this and would like the opinion of some people who have done this and have experience. Thank you for your time!
travelgravel is offline   Reply With Quote
Old 03-20-2019, 05:47 PM   #2
JDOnTheGo's Avatar
Coachwork: MCI
Chassis: 102 EL3
Engine: DD 60
I've only got a few minutes so will touch on a few things. Please don't consider this a 'complete' response. Hopefully enough to get things rolling...
Given the way you have things wired, I will assume that your inverter does not have an internal transfer switch. A transfer switch (internal or external) is not 'required' but, IMO, it the best approach - and not even all that expensive. Manually switching things will work - until you forget or someone attempt to 'help' (or whatever). A transfer switch avoids all that (something like this: https://amzn.to/2Fh25lR).
A fuse/circuit breaker between your solar panels and charge controller is needed as is one between the charge controller and battery. Using circuit breakers is handy as they can also (easily) serve as a switch when needing to power things down.
When dealing with both AC and DC, the term "ground" can become a bit confusing. With DC, you actually have a positive and negative lead. With AC, you have a 'grounding wire' (plus hot and neutral). That sometimes helps folks, sometimes not...
I'm not sure I understanding your 'grounding' questions so better let someone else take a shot.
See the above on 'grounding' confusion. A DC component must have a closed circuit (a lead for both positive and negative (to the battery in this case)). You can choose to use your chassis (for example) as a negative buss and then the batteries and all components (negative) are connected to this buss. However; that is often NOT recommended due to poor connections and loops. Regardless, all of the installations with which I am familiar connect the house battery bank negative to the chassis.
JD - Full timer out west
My Adventures & Build
Old 03-20-2019, 06:56 PM   #3
JDOnTheGo Thank you for your response! My inverter does not have an automatic transfer switch. I just ordered a transfer switch based on your recommendation. I will also get some breakers between the panels/charge controller and the charge controller/batteries.
From your last paragraph you are saying that some people only run hot(+) wires to their appliances i.e. water pump and the negative to the chassis of the bus? What I have done is run both hot(black) and negative/neutral(white) wires to all of my appliances and was going to attach those to my 12v fuse block which would then be attached to my batteries with some 6 gauge wire. Is what I have done the more correct way?
In response to the transfer switch I assume that it takes in the hot, neutral, and ground from both the inverter and shore power plug and outputs those into a single output of hot, neutral, and ground? Then this runs to the appliances. Where does the breaker box/Distribution panel factor in? Also does that ground that comes from the transfer switch need to be grounded to the bus bar or does the transfer switch itself get grounded to the bus bar?
Thanks again for your response!
*edit* I'm not sure how important it is but I forgot to mention that all outlets in the bus are GFCI outlets as well as the outlets on the inverter. I did not spring for GFCI circuit breakers in the breaker box. Should I?
Old 03-21-2019, 02:34 PM   #4
JDOnTheGo's Avatar
Coachwork: MCI
Chassis: 102 EL3
Engine: DD 60
Yes. I'm a red=positive, black=negative wire guy but the wire color doesn't affect performance. Running the negative back to the battery negative is best practice. This can be done with one or more hops thru buss bars (and appropriately larger wires/cables depending on the current that is being carried). This is also true of the positive. Sometimes in our very long buses, it is easier/better to run a large gauge wire (positive always fused, to protect the wire) from battery to a fuse block/circuit breakers located near the accessories/components and then branch off smaller gauge wires from there.
Correct.
The output from the transfer switch goes to your breaker box/panel. The output from each breaker goes to the appliances/plugs/etc. This way, the wire is protected by the circuit breaker regardless of whether it is powered from shore power or inverter.
...all outlets in the bus are GFCI outlets as well as the outlets on the inverter. I did not spring for GFCI circuit breakers in the breaker box. Should I?
As I understand it, you don't need both: https://www.thespruce.com/install-gf...reaker-1152797
Old 03-21-2019, 04:53 PM   #5
ermracing's Avatar
Engine: DT466E (195hp, 520tq)
Maybe this was mentioned and I missed it, but does your charger accept a 110 input to charge the batteries? The one we bought (still in a box) takes input from the solar panels, shore power and the alternator to charge the batteries. If that's the case, your 30amp shore power would be on the other side of the batteries.
Dave
Old 03-21-2019, 07:32 PM   #6
Hmmm, so If I have both the positive and negative wires coming from the battery that are attached to the 12v fuseblock one of those wires can be ran through a bus bar to ground the DC circuit? Does it matter if it is a different bus bar than the one that the AC circuit is grounded too?
No, I dont think so. My charge controller only has inputs for the batteries and the solar panels
Old 03-22-2019, 06:34 AM   #7
JDOnTheGo's Avatar
Coachwork: MCI
Chassis: 102 EL3
Engine: DD 60
I may be reading too much into your question. For an AC circuit, all three wires are connected inside the AC breaker panel. The panel itself is bonded to the chassis. For a DC circuit, the negative wire from an accessory may connect to a buss bar which is then connected to the battery bank negative. Yes, both AC and DC is typically bonded to the chassis.
If you need to charge the battery bank from shore power, you will need a charger. In the RV world, most of them are listed as "converter/chargers" - some are combined with an inverter (inverter/charger). I've had excellent results with the Progessive Dynamics products (like this: https://amzn.to/2OjpmaV). Like the charge controller, the charger/converter is 'smart' and charges the battery bank appropriate to its SOC (at least three, preferably four stages). As you can imagine, the "ideal" charger varies based on the size of your battery bank, voltage, etc.
Old 03-30-2019, 02:36 PM   #8
I've been trying to research this for the past few days and there is a loooot of conflicting information out there, but from what I have finally been able to piece together (please someone correct me if I'm wrong, I don't want people getting hurt):
DC "ground" is the negative, this gets attached to chassis
AC ground gets attached to chassis
AC negative does NOT get attached to chassis, and does NOT get attached to AC ground, you want a "floating neutral"
diannetea is offline   Reply With Quote
Old 03-30-2019, 02:49 PM   #9
negatives should always be grounded. So AC negative is the same as AC ground
Old 03-30-2019, 03:07 PM   #10
Thanks, I'm still reading and I think my misunderstanding stemmed from 1. really old threads from various sources, and 2. the fact that I didn't realize inverters will change the ground source when plugged in to shore
Everything I read says to keep the AC and DC grounds separate, but should you also keep the AC neutral and ground separate? So neutral to a bus bar, ground to a bus bar, and then those each would go to chassis?
Old 03-30-2019, 05:44 PM   #11
Hmmmm... which is the "negative" in an AC circuit......
Old 03-30-2019, 06:25 PM   #12
See what happens after smoking a fat one.
Hot, neutral and ground
Old 03-30-2019, 07:06 PM   #13
I think that's my fault, you were just responding using my bad terminology.
Maybe watching videos will help more than reading
Old 03-30-2019, 07:15 PM   #14
My fault for perpetuating your bad terminology
Old 03-30-2019, 07:38 PM   #15
roach711's Avatar
Rated Cap: 19
Your bus AC breaker panel should be a "branch panel" with separate ground and neutral bus bars. AC grounds and neutrals should be bonded (be attached at the same bus bar) only at the shore power panel.
The AC power panel should be grounded to the bus body in order for the breakers to function in the case of a loose hot wire touching the body.
AC neutrals do not ground to the chassis.
The ground wire in a DC circuit is simply completing the circuit, similar to the neutral wire in an AC circuit. The ground wire in an AC circuit is a safety feature that allows the breakers to do their job. Unless there is a short in the wiring there should never be voltage on an AC ground wire.
The Roach Motel
Old 04-04-2019, 09:46 PM   #16
Thank you. This like, semi made sense to me, but in my quest for more information I decided to read through the manual of the inverter I'm interested in eventually putting in my someday bus (lol), and this image really tied what you said together for me:
Old 04-04-2019, 11:12 PM   #17
roach711's Avatar
Rated Cap: 19
In the past I've had quite a bit of experience with residential AC circuits and working on engines made DC circuits familiar. What gave me fits was understanding how to get them both to coexist in the same vehicle. It's a steep learning curve.
The Roach Motel
Old 04-04-2019, 11:31 PM   #18
The only thing I know is you're not supposed to cross the wires
That being said I have a teeny bit of hands on experience from building a kitchenette for my son in 2017 that has lights in the fridge and oven, and the burners light up too. IIRC all of the lights were DC, and the burners were el leds (glued in a spiral to CDs) with a small DC inverter to make them work. Somehow figured out how to do it all so I'm sure I'll manage this too
Old 04-05-2019, 10:53 AM   #19
Mountain Gnome's Avatar
Chassis: TC1000 HandyBus
Rated Cap: 26 foot
AC stands for alternating current. The positive and negative poles alternate. One wire is hot, and its polarity alternates between + positive and - negative. The other wire is neutral and completes the circuit. The ground wire in an AC setup is not part of the circuit, but a backup to keep you from getting a deadly shock.
DC stands for direct current. The positive and negative poles are dedicated and do not change. In most modern vehicles, the positive pole is "hot," that is the current flows from the + to the - pole.
Old 04-07-2019, 05:38 AM   #20
Coachwork: Bluebird, Collins
A very handy tip: For low voltage DC (12-24 volt systems) disconnects one can use ordinary Square D Type QO circuit breakers and enclosures available at any big box hardware store. Don’t use Square D Homeline breakers. They don’t have a DC rating like Type QO. Otherwise special DC breakers need to be ordered or fuses used. These high voltage breakers are only necessary if the panels are in higher voltage strings.
Enjoy your new power system
Doktari is offline   Reply With Quote