Excel over pressurizing?

Hi everyone,

Thanks in advance for your help.

We have the Excel tankless ventless hot water heater in our skoolie and have been experiencing some issues I'm hoping someone out there can help us trouble-shoot.

1. The water heater occasionally shoots out super heated water from the water drain. About 1/2 c. to 1 c. comes out when it does this.
2. Sporadically the flame doesn't turn off when we turn the water off. I believe this is why the water is getting super heated.
3. Yesterday, the hot water pipe (PEX) coming out of the tank burst. When it burst i had been running the hot water in the sink and noticed it wasn't getting very hot. I probably ran 2 gallons of hot water before turning it off. I can't remember for sure whether I turned the water off and then the pipe burst or the pipe burst and then I turned the water off because it was basically at the same time.

other info: The pipes have not been exposed to freezing temperatures. the water heater has been in use for about 2 months now.

Any ideas?

is there something we should know about the set up that we could have done wrong?

Thanks so much for your help!

epaashaus is offline   Reply With Quote
Old 02-20-2019, 02:37 PM   #2
Bus Geek
 
ol trunt's Avatar
 
Join Date: Apr 2012
Location: So Cal
Posts: 3,231
Year: 1935
Coachwork: Superior
Chassis: Chevy
Engine: 317 ci/tid / Isuzu
My best advice is to send the heater back to the mfg for repair and don't risk a steam boiler explosion.
Jack
ol trunt is offline   Reply With Quote
Old 02-20-2019, 04:07 PM   #3
Bus Geek
 
Jolly Roger bus 223's Avatar
 
Join Date: Sep 2017
Location: Swansboro,NC
Posts: 2,988
Year: 86
Coachwork: Thomas
Chassis: Ford B700
Engine: 8.2
Rated Cap: 60 bodies
Sounds like the thermostat or control board isn't working properly.
If it is still under warranty then try to get it replaced or repaired before using it again.
The P&T (pressure and temperature ) relief valve is doing its job if it's spitting extremely hot water. Any time it is doing its job then there is a problem somewhere. I haven't used a lot of PEX butThere is a red pex rated for hot water use.
In my thinking anything plastic is not going to handle 180-210degree water if the water heater mucks up.
If it's not under warranty then find the owners and parts manual for it and PM me.
Should be able to help fix it.
Jolly Roger bus 223 is offline   Reply With Quote
Old 02-20-2019, 04:16 PM   #4
Bus Geek
 
o1marc's Avatar
 
Join Date: Dec 2017
Location: Dawsonville, Ga.
Posts: 10,482
Year: 1999
Coachwork: Genesis
Chassis: International
Engine: DT466/3060
Rated Cap: 77
Quote:
Originally Posted by Jolly Roger bus 223 View Post
Sounds like the thermostat or control board isn't working properly.
If it is still under warranty then try to get it replaced or repaired before using it again.
The P&T (pressure and temperature ) relief valve is doing its job if it's spitting extremely hot water. Any time it is doing its job then there is a problem somewhere. I haven't used a lot of PEX butThere is a red pex rated for hot water use.
In my thinking anything plastic is not going to handle 180-210degree water if the water heater mucks up.
If it's not under warranty then find the owners and parts manual for it and PM me.
Should be able to help fix it.
They are all rated for hot water use. The color of the Pex is to distinguish hot and cold. There is no difference between the Red, Blue, White, and Gray Pex. They are only rated to 200°F.
o1marc is offline   Reply With Quote
Old 02-20-2019, 04:33 PM   #5
Bus Geek
 
Jolly Roger bus 223's Avatar
 
Join Date: Sep 2017
Location: Swansboro,NC
Posts: 2,988
Year: 86
Coachwork: Thomas
Chassis: Ford B700
Engine: 8.2
Rated Cap: 60 bodies
Thanks for the info. I didn't know the temp. And pressure rating of the material itself.
I have a few tools to repair some of it but have never ran it.
I have always worked as a commercial installer for the GOVT. so my minimum for domestic water is copper.
Thanks Marc.
For the OP. I don't know your brand of heater but I have worked on many other brands and they are not that complicated.
If you can't get a warranty fix then get us the info. And we can help.
Jolly Roger bus 223 is offline   Reply With Quote
Old 02-20-2019, 05:00 PM   #6
Bus Geek
 
o1marc's Avatar
 
Join Date: Dec 2017
Location: Dawsonville, Ga.
Posts: 10,482
Year: 1999
Coachwork: Genesis
Chassis: International
Engine: DT466/3060
Rated Cap: 77
Quote:
Originally Posted by Jolly Roger bus 223 View Post
Thanks for the info. I didn't know the temp. And pressure rating of the material itself.
I have a few tools to repair some of it but have never ran it.
I have always worked as a commercial installer for the GOVT. so my minimum for domestic water is copper.
Thanks Marc.
For the OP. I don't know your brand of heater but I have worked on many other brands and they are not that complicated.
If you can't get a warranty fix then get us the info. And we can help.
One advantage of Pex over copper is the fact it can be radiused, so fewer sweat connections to possibly leak.

Here's some pressure/temp info;
Pressure ratings, testing and pressure drop
PEX Tubing Pressure Ratings Pressure testing - Hydronic & Radiant Heating Pressure testing - Hot & Cold Water Plumbing
200°F at 80 psi
180°F at 100 psi
74°F at 160 psi 3 times the maximum working pressure or a minimum of 40 psi, but no greater than 100 psi.

Duration: 30 minutes minimum, 2 hours recommended 1.5 times the maximum working pressure but no greater than pipe’s pressure rating at given temperature.

Duration: 30 minutes minimum, 2 hours recommended
o1marc is offline   Reply With Quote
Old 04-09-2020, 12:08 PM   #7
Bus Crazy
 
david.dgeorge07's Avatar
 
Join Date: May 2017
Location: Chattanooga, TN
Posts: 1,413
Year: 2001
Coachwork: Thomas
Chassis: Thomas
Engine: CAT 3126
I have had the same problem with my Excel 1.6 Gpm tankless heater. Blown out pex 2x now resulting in major flooding. Loud bang after turning off water - flame continues to burn superheating the water. Not good. Working with the company now to try to see what repair to the unit is possible to fix this. Makes me not want to use this type of heater anymore. If I do use again I think I'll install emergency propane and water shutoff valves next to the heater.

Here's my opinion: the super low flow magnetic flow sensor that they tout in their description is too sensitive and is malfunctioning. I don't really need the thing to work with only 2psi. I need it to NOT EXPLODE with normal use!
__________________
My Build Thread:

https://www.skoolie.net/forums/f11/4-...ner-18205.html
david.dgeorge07 is offline   Reply With Quote
Old 04-09-2020, 07:07 PM   #8
Mini-Skoolie
 
Join Date: Feb 2020
Location: Canton Tx, 100mi east dallas
Posts: 35
Year: 2005
Coachwork: startrans
Chassis: e450
Engine: 7.2 turbo diesel
following, have the heater in my amazon cart, just making sure I have all I need before hitting send. anybody else have experience with one
besterfe is offline   Reply With Quote
Old 05-17-2023, 07:03 PM   #9
Skoolie
 
Join Date: Jun 2019
Location: Lebanon, IN
Posts: 153
Year: 2003
Coachwork: AmTran
Chassis: International
Engine: DT466e/Allison 2000
Rated Cap: 65
Just had this exact scenario happen to me. Took a shower, just as i turned the shower valve off there was an explosion. Thought it was propane at first but quickly realized it was the water line. Pex line, blew a hole about 1" below the outlet for the water heater. Unnerving for sure. Wife is very afraid now.
cdrobbins77 is offline   Reply With Quote
Old 05-18-2023, 06:03 AM   #10
Bus Nut
 
La Camioneta's Avatar
 
Join Date: Mar 2022
Location: CSRA Georgia
Posts: 394
Year: 1994
Coachwork: Blue Bird
Chassis: Ford B-700
Engine: 12V 5.9
Is the consensus that the hot water output pipe should be a few feet of copper at least? Then once out of the overheat zone go to pex?
La Camioneta is offline   Reply With Quote
Old 05-18-2023, 06:21 AM   #11
Skoolie
 
Join Date: Jun 2019
Location: Lebanon, IN
Posts: 153
Year: 2003
Coachwork: AmTran
Chassis: International
Engine: DT466e/Allison 2000
Rated Cap: 65
Quote:
Originally Posted by La Camioneta View Post
Is the consensus that the hot water output pipe should be a few feet of copper at least? Then once out of the overheat zone go to pex?
I can tell you if I do another build I will use copper for at least a foot on the output side, but in my current build it would be way too much effort to change it out at this point. So I just replaced mine with pex again. 🤞
cdrobbins77 is offline   Reply With Quote
Old 05-18-2023, 10:17 AM   #12
Bus Crazy
 
DeMac's Avatar
 
Join Date: Oct 2020
Location: Florida
Posts: 1,570
Coachwork: Integrated Coach Corp.
Chassis: RE-300 42ft
Engine: 466ci
Rated Cap: 90
18" Cu Stubs

Quote:
Originally Posted by La Camioneta View Post
Is the consensus that the hot water output pipe should be a few feet of copper at least? Then once out of the overheat zone go to pex?
-----------------


(18" Minimum, 24" better, imo. To help ensure >6" gap between the fittings & the vent)
__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -5. The time now is 01:23 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.