Has anyone done something like this? We are willing to have a generator as backup for days with low sun. But would the battery be enough to keep the AC on for the night?
|
I have three of the aforementioned Tesla batteries in my rig. There are a few factors that play into this:
First, Tesla batteries are an array of 444 18650's in 6s74p configuration. 6s puts these "24v" batteries in the lower 24V spectrum- they're 3 ish volts lower than an AGM/lead acid 24V bank, and 6ish volts lower than a 48V bank. This means two things:
1) You NEED to charge them to voltages appropriate to their 6S configuration (25.5V in 24V config,, or 51.5V in 48V config maximum)
2) You NEED to balance them. If you charge the pack to 25V and one cell in the series is at 4.5V, you are damaging that cell.
3) Because of their lower voltage, most inverters will not be able to use their full capacity, cutting off at around 30-40%. 24V AGM banks range from 22V- 28.8V while these range from 19.8V-25.5V.
I saw a youtube video of a guy who put one of these in their rigs with what looked like no balancer and completely inappropriate wiring/etc. The day they moved in the lights went out for good and it was game over for them. The guy made lots of mistakes...
What really matters is maximum draw/wattage. This 9k split is what I want:
https://www.ebay.com/itm/9000-BTU-37...cAAOSwxHlcWaYh
According to the spec sheet, 500W is the rated input (maximum). Which means in theory I can run the unit at full tilt for ~10H, multiply that by 65% because of the battery's usable capacity with my inverter, is 6H per battery. I have three, so 18H of runtime at _full_ capacity AND at the max draw rating of the unit.
In the real world, I'd see > 24H runtime: I have good insulation, the unit will not always be running at its maximum rating, and even though I have other appliances, etc, most of my electrical is DC and quite power efficient. The biggest influence for me on runtime is how much I do laundry.
I plan on 2000W in panels, which should make up for any losses at night and then some on decently sunny days.