Old 12-25-2014, 08:30 PM   #61
Skoolie
 
Join Date: Dec 2014
Posts: 170
Floating ground is when your ground does not have a physical connection to the earth. As in an RV, its grounded to the chassis. Still plenty of steel to dissipate whatever current you'd be running without worry about you being the ground instead... unless we're talking about some serious voltage, lightning for instance.

You run into safety issues when you have a poor ground and you are the path of least resistance instead of the bus.

__________________
https://www.skoolie.net/forums/showthread.php?t=9883 - 7.3L 4x4 Shuttle Bus Toyhauler conversion
headinthetrees is offline  
Old 12-26-2014, 04:06 AM   #62
Site Team
 
Join Date: Jun 2014
Location: southwest lowsyana
Posts: 542
Year: 1988
Coachwork: ward
Chassis: international
Engine: dt360a
Rated Cap: 65
thanks. so a floating ground system is same as typical 12v automotive? the generator i bought has a tt-30 plug that states floating ground, and the breaker panel i got from a rv is wired where the grounds and neutrals are kept separate, but everyone has been telling me that my 110 side of my bus must be grounded.............im confused!
claydbal is offline  
Old 12-26-2014, 12:35 PM   #63
Skoolie
 
Join Date: Dec 2014
Posts: 170
Yes automobiles use floating grounds. You get into issues when you have multiple grounds and multiple sources of power. Basically you just want to make sure your ground is coming from the same place as your power feed. You can test resistance of your ground to make sure its adequate (lower is better), but not having much experience with rv's and DC systems I can't confidently suggest what is an acceptable threshold.
__________________
https://www.skoolie.net/forums/showthread.php?t=9883 - 7.3L 4x4 Shuttle Bus Toyhauler conversion
headinthetrees is offline  
Old 01-24-2015, 08:45 PM   #64
Bus Nut
 
Join Date: Oct 2011
Location: Snowflake, Arizona
Posts: 343
Year: 1996
Coachwork: Blue Bird
Chassis: All American Rear Engine
Engine: C-8.3-300 Cummins MD3060
Rated Cap: 40 Prisoners
Setting up Bus A/C

Ok I have these components 50 Amp power panel, 30Amp power panel Automatic transfer switch 50 Amp, 10K diesel generator presently set up
as 120 volt only plus a 4k inverter charger with auto transfer relay built in as well as auto generator start switch. I would like to use the power panel 50 amp for shore power input running thru the transfer switch 50 amp to the power panel then have the other side of the transfer connect both buses of
the panel together to run off of 120 volt from the generator. Question is
should I have a manual switch or something fail proof to prevent shorting the two buses together when plugged into shore power? The Inverter charger will be mounted further down the line coming out of the main panel and feed into the 30 amp sub panel for protection. Having hard time figuring out a proper diagram for my setup so here I am approaching the Guru for
greater knowledge and enlightenment.
Dragonpop is offline  
Old 03-09-2015, 03:25 AM   #65
Mini-Skoolie
 
Join Date: Feb 2015
Posts: 20
Year: 81
Chassis: Crown Supercoach
Engine: 885 Cummins Turbo (A-855t-11)
Hello all. I have been lurking on this site since last year and this is my first post. I Purchased a 1981 crown 855 turbo cummins, in september of last year and have been converting it since. I have now come to the time where I will be running my electrical.

I will be purchasing solar panels and will have a battery bank and an inverter. I am running 10gauge direct bury wire for my 120 volt appliances as I had some left over from a previous project. I ran this above my insulation on the floor and below my hardwood floor I just installed unfortunately I was unable to put it through conduit but it being direct burial I think it should be ok ( though i know more prone to vibrational wear). This one 10 gauge wire will operate a 6amp freezer and a 5amp freezer converted to a kegerator

I have some basic knowledge of electricity about breakers and wire gauge and such wiht AC but not any with DC or with an RV. I purchased a cummins marquis gold 5500 and will have solar panels installed as well with a battery bank

I have done a lot of reading but want to get some direct input.

#1 Will grounding the AC and DC to the chasis interfere with each other?(Can I ground my inverter and DC circuit and generator to the chasis?)

#2 the generator came with a transfer box for shore power. I was reading previously in this thread about being able to bond and unbond your neutral and your ground. What exactly does that mean and how does one do that? What exactly does this transfer box do ?

#3 In terms of circuit breaker box I will want a 30 amp breakers since I am running 10 gauge wire. Do those wires all connect in breaker box and then a larger gauge wire that can hand all of my loads at once comes out of the breaker box and to the inverter. Where does a GFCI get installed?

#4 Can I run DC power cables alongside AC power cables?


Thanks

HR
HunteR0se is offline  
Old 03-09-2015, 06:43 AM   #66
Bus Geek
 
EastCoastCB's Avatar
 
Join Date: Sep 2014
Location: Eustis FLORIDA
Posts: 23,764
Year: 1999
Coachwork: Thomas
Chassis: Freighliner FS65
Engine: Cat 3126
Rated Cap: 15
Welcome,
So you have a Crown? We will need pics!
EastCoastCB is offline  
Old 03-09-2015, 08:19 AM   #67
Bus Nut
 
Join Date: Feb 2015
Posts: 258
Quote:
Originally Posted by HunteR0se View Post
#1 Will grounding the AC and DC to the chasis interfere with each other?(Can I ground my inverter and DC circuit and generator to the chasis?)
You don't have a choice. For safety reasons you really need the biggest, most available chunk of ground material (the chassis) to be the "ground" in your AC system. It is possible to pick up some noise this way, but in practice this is less of a big deal than a lot of people think. A bus is a HUGE ground path.

Quote:
Originally Posted by HunteR0se View Post
#2 the generator came with a transfer box for shore power. I was reading previously in this thread about being able to bond and unbond your neutral and your ground. What exactly does that mean and how does one do that? What exactly does this transfer box do ?
Electrical boxes (usually) have two bus bars, bars with lots of holes and screws to attach neutrals and grounds to (the hots go to the breakers, of course). "Bonding" means the neutral and ground are tied together. This is the default in a lot of cases. However, NEC calls for some circuit configurations to be "unbonded", which means the connection between the two needs to be separated.

The circumstances in which this is required aren't 1-sentence-summary material. The ultimate goal is to make sure the ground wire is always "available" for its safety purpose and not actually carrying current at any one time. You should be able to grab ahold of it and not get electrocuted, even sitting in a bathtub full of water. That's why it's usually bare, not insulated - it's supposed to be a safety wire, not a current-carrying wire.

Neutral IS a current-carrying wire. They're tied together at the main panel in a house, for example, because that's the final exit point of electricity. There's a ground rod tied in there, too. Few houses actually have a true "neutral" out to the pole, especially in the US. If you look at the wire into your house you'll see it's actually just two conductors, one for each side of 240V. Your ground rod creates a "center tap" between the two that lets you get 120V out of each. Those wires to the pole aren't hot and neutral - they're both hot. And the steel carrier cable isn't hooked up to anything.

Anyway, that means neutral and ground are the SAME THING in the main panel in your house - and probably should be in your RV, too. But only at that one location. In almost all configurations, everything downstream (sub-panels, other boxes, etc.) should be "unbonded". Current should never be allowed to jump from neutral to ground anywhere other than at that panel. The reason is that if your neutral breaks (and wire breakage is one of the main failure modes these things are designed to deal with), you do NOT want current jumping over onto the ground wire and making that, essentially, a "hot" wire on the way back to the panel. Fires, electrocution, and other unreasonably nasty things await.

I haven't even begun to get into how this is all supposed to work - I'm paraphrasing, and I'm not even an electrician myself. If you're at ALL less than 100% certain how this should all be wired, consult one! Most charge < $100/hr, and since you aren't going to be getting a CO for this stuff, an hour or two of consultation is probably all you need - they're not going to sign off on anything. It's totally worth it.

Quote:
Originally Posted by HunteR0se View Post
#3 In terms of circuit breaker box I will want a 30 amp breakers since I am running 10 gauge wire. Do those wires all connect in breaker box and then a larger gauge wire that can hand all of my loads at once comes out of the breaker box and to the inverter. Where does a GFCI get installed?
A GFCI can be installed anywhere - it's usually point-of-use (in the bathroom, kitchen, etc.) There are GFCI devices that can "chain" or be installed "upstream" - examine your device for installation instructions.

Yes, your upstream wire needs to be able to handle the total capacity of what's in the panel.

Quote:
Originally Posted by HunteR0se View Post
#4 Can I run DC power cables alongside AC power cables?
Yes, but the further apart, the better. Actually, it turns out to be more important to consider where they CROSS than where they run PARALLEL for very long-winded explanations I won't get into here (but a CAT5 cable installer knows all about). A few inches apart is actually remarkably good at isolating noise. If you're really concerned, throw in a few lengths of EMT conduit. It's cheap, easy to cut, and if you ground one end (JUST ONE END) is a very effective noise isolator.

Grounding both ends can make ground loops - do not do this thinking it will be better.
taskswap is offline  
Old 03-09-2015, 06:47 PM   #68
Bus Nut
 
PDBreske's Avatar
 
Join Date: Sep 2010
Location: Ocala, FL
Posts: 635
Year: 1995
Coachwork: Bookmobile body by Farber
Chassis: International 3800
Engine: Navistar DT466/Alison MT643
Rated Cap: 1
Quote:
Originally Posted by taskswap View Post
... and if you ground one end (JUST ONE END) is a very effective noise isolator.

Grounding both ends can make ground loops - do not do this thinking it will be better.
In my system, I attached the green ground wire to the ground bar inside the circuit breaker box and the other end to each metal outlet box and the ground connection on the outlet itself. The breaker box is grounded only to the inverter, which picks up the ground from the shore feed when I'm plugged in.

At least three of my outlet boxes are also attached to the metal skin of the bus. I have used tools and lights plugged into these outlets, but so far have not had any problems.

Should I go back and somehow isolate those boxes from the outer skin to prevent a ground loop? Or am I misunderstanding this whole concept?
PDBreske is offline  
Old 03-09-2015, 08:05 PM   #69
Bus Nut
 
Join Date: Feb 2015
Posts: 258
No, not unless you have a lot of system "noise" on your radio. Ground loops are the things that give you "alternator whine" when you're driving. No problem => no change.

My point was more about how electrical systems are full of misunderstandings. You figure, hey, it's a shield. I should ground it everywhere, right? But what happens is some ground current ends up flowing through the shield itself, and then it's not a shield any more - or worse, it's an antenna. Counter-intuitive, but...

Technically, if you have metal electrical boxes attached to the metal of the bus with a good connection, and so is your breaker panel, you don't need a separate ground wire - and the NEC would say you're not supposed to install it (you use a ground in the wire bundle, OR ground the conduit at the upstream end - but not both). But all of this is for houses, and your setup isn't going to hurt anything. Just make sure you do provide a neutral. If your bus is a safety ground, don't use it as a return path, too.
taskswap is offline  
Old 03-10-2015, 01:24 AM   #70
Mini-Skoolie
 
Join Date: Feb 2015
Posts: 20
Year: 81
Chassis: Crown Supercoach
Engine: 885 Cummins Turbo (A-855t-11)
Task

Thanks for the lengthy response. I have another question that sort of related to PD's question. I was wondering if I could just ground he outlets to the bus skin right by the outlets since the whole bus skin is aluminum. Or even better there is a I want to say 12 or 14 gauge steel upside down L that the bus coving was attached to that runs down both sides of the bus and is wrapped by the aluminum inner skin of the bus. I was thinking this would be enough metal to dissipate the charge. I could then ground my battery bank to the chasis and there would be less interference....I think. What would be the advantages/disadvantages to doing this. What would happen if I did this for neutral instead of the ground and grounded the battery ground and the inverter ground to the Chasis instead? This would be bad right?

Eastcoast
We have been documenting the conversion and will post it up on here in the next month or so. It is in amazing condition and we have painted it green and kept the black stripes
HunteR0se is offline  
Old 03-10-2015, 09:06 AM   #71
Bus Geek
 
lornaschinske's Avatar
 
Join Date: Jun 2004
Location: Roswell, NM
Posts: 3,588
Year: 1986
Coachwork: BlueBird
Chassis: 40 ft All American FE
Engine: 8.2LTA Fuel Pincher DD V8
Rated Cap: 89
Buy.
The.
Book.
No Shock Zone
__________________
This post is my opinion. It is not intended to influence anyone's judgment nor do I advocate anyone do what I propose.
Fulltime since 2006
The goal of life is living in agreement with nature. Zeno (335BC-264BC)
https://lorndavi.wordpress.com/blog/
https://i570.photobucket.com/albums/s...ps0340a6ff.jpg
lornaschinske is offline  
Old 03-10-2015, 10:27 AM   #72
Bus Nut
 
Join Date: Feb 2014
Location: Cuyahoga Falls Ohio
Posts: 592
Year: 1997
Coachwork: Startrans
Chassis: Ford e-350 single wheel
Engine: 5.4 litre
Rated Cap: 12
Good write up except the for the service drop (3 wires coming in from the utility pole does have a bare neutral wire, it is not just for strain but an important part of your service. (at least in Wye system) Maybe a Delta system is different???
Quote:
Originally Posted by taskswap View Post
You don't have a choice. For safety reasons you really need the biggest, most available chunk of ground material (the chassis) to be the "ground" in your AC system. It is possible to pick up some noise this way, but in practice this is less of a big deal than a lot of people think. A bus is a HUGE ground path.



Electrical boxes (usually) have two bus bars, bars with lots of holes and screws to attach neutrals and grounds to (the hots go to the breakers, of course). "Bonding" means the neutral and ground are tied together. This is the default in a lot of cases. However, NEC calls for some circuit configurations to be "unbonded", which means the connection between the two needs to be separated.

The circumstances in which this is required aren't 1-sentence-summary material. The ultimate goal is to make sure the ground wire is always "available" for its safety purpose and not actually carrying current at any one time. You should be able to grab ahold of it and not get electrocuted, even sitting in a bathtub full of water. That's why it's usually bare, not insulated - it's supposed to be a safety wire, not a current-carrying wire.

Neutral IS a current-carrying wire. They're tied together at the main panel in a house, for example, because that's the final exit point of electricity. There's a ground rod tied in there, too. Few houses actually have a true "neutral" out to the pole, especially in the US. If you look at the wire into your house you'll see it's actually just two conductors, one for each side of 240V. Your ground rod creates a "center tap" between the two that lets you get 120V out of each. Those wires to the pole aren't hot and neutral - they're both hot. And the steel carrier cable isn't hooked up to anything.

Anyway, that means neutral and ground are the SAME THING in the main panel in your house - and probably should be in your RV, too. But only at that one location. In almost all configurations, everything downstream (sub-panels, other boxes, etc.) should be "unbonded". Current should never be allowed to jump from neutral to ground anywhere other than at that panel. The reason is that if your neutral breaks (and wire breakage is one of the main failure modes these things are designed to deal with), you do NOT want current jumping over onto the ground wire and making that, essentially, a "hot" wire on the way back to the panel. Fires, electrocution, and other unreasonably nasty things await.

I haven't even begun to get into how this is all supposed to work - I'm paraphrasing, and I'm not even an electrician myself. If you're at ALL less than 100% certain how this should all be wired, consult one! Most charge < $100/hr, and since you aren't going to be getting a CO for this stuff, an hour or two of consultation is probably all you need - they're not going to sign off on anything. It's totally worth it.



A GFCI can be installed anywhere - it's usually point-of-use (in the bathroom, kitchen, etc.) There are GFCI devices that can "chain" or be installed "upstream" - examine your device for installation instructions.

Yes, your upstream wire needs to be able to handle the total capacity of what's in the panel.



Yes, but the further apart, the better. Actually, it turns out to be more important to consider where they CROSS than where they run PARALLEL for very long-winded explanations I won't get into here (but a CAT5 cable installer knows all about). A few inches apart is actually remarkably good at isolating noise. If you're really concerned, throw in a few lengths of EMT conduit. It's cheap, easy to cut, and if you ground one end (JUST ONE END) is a very effective noise isolator.

Grounding both ends can make ground loops - do not do this thinking it will be better.
leadsled01 is offline  
Old 03-10-2015, 10:33 AM   #73
Mini-Skoolie
 
Join Date: Feb 2015
Posts: 20
Year: 81
Chassis: Crown Supercoach
Engine: 885 Cummins Turbo (A-855t-11)
lorn

thanks, did not know about THE BOOK
HunteR0se is offline  
Old 03-10-2015, 04:23 PM   #74
Bus Geek
 
Join Date: Aug 2011
Location: Stony Plain Alberta Canada
Posts: 2,937
Year: 1992
Coachwork: Bluebird
Chassis: TC2000 FE
Engine: 190hp 5.9 Cummins
Rated Cap: 72
I read the book too, years ago.

I will not use the body or any metal of the bus as a ground. All grounds will be isolated from the metal in the bus.

I will be using all plastic boxes. No metal.

Every wire will be in plastic conduit.

The way most RV's are grounded is poor at best. I will be using a ground plate in the moist earth, or a ground plate submerged into a pond for a good ground.

If you don't connect any grounds, ect to your bus, you will have no chance of hot skinning. A energized bus is the last thing I want.

Nat
__________________
"Don't argue with stupid people. They will just drag you down to their level, and beat you up with experience."

Patently waiting for the apocalypses to level the playing field in this physiological game of life commonly known as Civilization
nat_ster is offline  
Old 03-10-2015, 06:32 PM   #75
Skoolie
 
Join Date: Aug 2010
Posts: 147
Year: 1993
Coachwork: Bluebird
Chassis: TE2000 FE
Engine: 5.9L Cummins
Rated Cap: 84
Lets see if I can explain this clearly. Disclaimer: I am not saying anyone is wrong or right. Just there is a right way and a wrong.

1. If you are boondocking your power source is you. Meaning your power comes from batteries, or solar, or generator, or squirrels in a cage on a wheel. The DC system must be complete, including a ground back to the source. No ground no worky. The AC system must have a neutral to return to the system and a ground to protect it.

2. In modern AC systems you must have a hot, neutral, and ground. Hot supplies power to what ever, neutral is the return side in a modern system, ground protects you and your love ones. So by all means do you proper grounding, ground to the chassis.

3. Fuses are designed to protect the circuit not the user. The ground is meant to protect you. If you eliminate the ground we have fried person. If a short occurs then the ground now works as the return for the power and fuse blows as current is excessive and this saves people because shorts don't live with grounds.

4.Neutrals should be controlled by your inverter, (note to self: if you don't have one you wont have a safe boondocking AC system). All quality mobile inverters have a neutral switching provision. This means when boondocking the inverter takes care of the proper bonding issue. When you start you gen set, it again takes care of your proper bonding and yes when you plug in at the camp ground (after checking your site plug in) it again does its job.

In summary its my opinion that chassis ground is required for both AC and DC. If you are going to bother to build your way skimp on anything but the inverter (again my opinion). If you want to skimp on the inverter then learn how to make a relay controlled neutral switching circuit for neutral bonding. Before you by that fancy inverter gen set remember they do not bond neutral correctly and see above recommendation on cheap inverters.
Lastly yes you can have a different opinion then me, Its okay to be different after all we are skoolies.

Have a great day
Chuck
cschlessman is offline  
Old 03-10-2015, 07:00 PM   #76
Bus Nut
 
Join Date: Feb 2015
Posts: 258
What he said. Also, those "quality" inverters deal with phase-matching, too...≈
taskswap is offline  
Old 03-11-2015, 12:07 AM   #77
Bus Geek
 
lornaschinske's Avatar
 
Join Date: Jun 2004
Location: Roswell, NM
Posts: 3,588
Year: 1986
Coachwork: BlueBird
Chassis: 40 ft All American FE
Engine: 8.2LTA Fuel Pincher DD V8
Rated Cap: 89
Quote:
Originally Posted by nat_ster View Post
I read the book too, years ago.

Nat
Really? "No Shock Zone" publish date was Jun 16, 2014
__________________
This post is my opinion. It is not intended to influence anyone's judgment nor do I advocate anyone do what I propose.
Fulltime since 2006
The goal of life is living in agreement with nature. Zeno (335BC-264BC)
https://lorndavi.wordpress.com/blog/
https://i570.photobucket.com/albums/s...ps0340a6ff.jpg
lornaschinske is offline  
Old 03-11-2015, 09:44 AM   #78
Bus Geek
 
Join Date: Aug 2011
Location: Stony Plain Alberta Canada
Posts: 2,937
Year: 1992
Coachwork: Bluebird
Chassis: TC2000 FE
Engine: 190hp 5.9 Cummins
Rated Cap: 72
Quote:
Originally Posted by lornaschinske View Post
Really? "No Shock Zone" publish date was Jun 16, 2014
Really, I see a 2010 copy right.



Nothing about electricity has changed recently, so why do we need new publications? Just one more interpretation of the same thing.

Grounding any of the AC power to the metal of the bus is a mistake IMO.

Why would you take the chance of energizing the metal skin of your bus?

Residential electrical is always properly grounded with a ground rod, or ground plate. What is wrong with doing this in your skoolie?

My stabilizer jacks are steel and touch the ground, unless I set them on a wood block. This is essentially a ground. However, not a adequate ground IMO.

Residential AC systems don't have a ground running from the transformer to the house, only two hot leads. Grounding is done at the house with a ground rod, or ground plate.

Many industrial systems don't even use grounds. They are far more reliable this way.

All my DC grounds including the buses wiring harness will also be isolated from the buses metal body. This makes for less electrolysis (RUST), and a safer, more reliable DC system.

My inverter will be far from cheap. It has what is necessary for the neutral bonding.

As long as your grounding your AC to your metal bus, you risk electrocution. All it takes is one wire in your shore cable to become damaged, or a faulty wired item to be plugged in.

Like it's been said on here. The ground is the safety for the user. Please be safe.

Nat
__________________
"Don't argue with stupid people. They will just drag you down to their level, and beat you up with experience."

Patently waiting for the apocalypses to level the playing field in this physiological game of life commonly known as Civilization
nat_ster is offline  
Old 03-11-2015, 10:12 AM   #79
Bus Nut
 
Join Date: Feb 2014
Location: Cuyahoga Falls Ohio
Posts: 592
Year: 1997
Coachwork: Startrans
Chassis: Ford e-350 single wheel
Engine: 5.4 litre
Rated Cap: 12
I personally don't like ungrounded systems, although they do have some good. Navy Veteran here. All US Naval ships are ungrounded systems and well really suck as far as electrical goes. And have you ever worked on an old Corvette electrical system. Arrrgghhhh... Just my opinion here...
leadsled01 is offline  
Old 03-11-2015, 11:37 AM   #80
Bus Geek
 
lornaschinske's Avatar
 
Join Date: Jun 2004
Location: Roswell, NM
Posts: 3,588
Year: 1986
Coachwork: BlueBird
Chassis: 40 ft All American FE
Engine: 8.2LTA Fuel Pincher DD V8
Rated Cap: 89
Quote:
Originally Posted by nat_ster View Post
Really, I see a 2010 copy right.

Nat
Those are the online articles. The book is much later...
http://www.amazon.com/No~Shock~Zone-...=no+shock+zone

Paper back has an Aug 2, 2014 date

You are the reason I first posted links to No Shock Zone in RV Electrical Safety.
__________________
This post is my opinion. It is not intended to influence anyone's judgment nor do I advocate anyone do what I propose.
Fulltime since 2006
The goal of life is living in agreement with nature. Zeno (335BC-264BC)
https://lorndavi.wordpress.com/blog/
https://i570.photobucket.com/albums/s...ps0340a6ff.jpg
lornaschinske is offline  
Closed Thread

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bus Electrical Systems - DC Les Lampman Conversion Tutorials and How-to's 65 12-13-2016 05:49 AM
Leveling systems lornaschinske Conversion General Discussions 0 08-04-2012 10:42 AM
Electrical Systems noahyay Conversion General Discussions 11 07-29-2005 05:43 AM
Sewer Systems Steve Conversion Tutorials and How-to's 0 06-16-2004 12:31 PM

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -5. The time now is 10:42 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.