We've framed enough of the ceiling to install the overhead Electrical rough-in. The permanent wire structure is being used for our temporary lighting, while we build. I'll document our process in this thread.


I'll briefly cover the ceiling framing we chose. A simple process repeated often at skoolie.net, neither unique or complex.

Overhead Electrical Rough-in includes any overhead raceways & wiring.

Usually lighting, switchlegs, rooftop A/Cs, exaust fans, ceiling recepticals, smoke & CO2 detectors, sign or flood lights. Overhead often includes low voltage & communications, which I'll complete separately.


The high voltage wire methods used on Freddy D are commercial grade. Steel armored cable, steel boxes, steel fittings, steel supports.

__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Old 06-19-2022, 12:54 PM   #2
Bus Crazy
 
DeMac's Avatar
 
Join Date: Oct 2020
Location: Florida
Posts: 1,570
Coachwork: Integrated Coach Corp.
Chassis: RE-300 42ft
Engine: 466ci
Rated Cap: 90
Tek Screws & Lumber

JakeSales.com has a large selection of fasteners.



This 270 ct box was about $50
Wood to Metal framing screws
#12 x 2-1/2" Reamer Tek Star/Torx T-30 Screw Head

Self-Drilling Wood to Metal Screws for Flatbeds, Trailers, or for Fastening Wood to Steel



To prevent lifting, the screws' tabs ream the wood to 7/16", then break away as they hit the steel. The tip drills the steel, then taps/threads the hole to 24 tpi. The countersink head design even cuts it's own recess. Speedy.

To stay perpendicular, we predrilled our wood framing with 3/8" pilot holes.


Ceiling framing lumber, two by three (1.5" x 2.5" actual) supported using two tek screws at each rib.
__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Old 06-19-2022, 01:19 PM   #3
Bus Crazy
 
DeMac's Avatar
 
Join Date: Oct 2020
Location: Florida
Posts: 1,570
Coachwork: Integrated Coach Corp.
Chassis: RE-300 42ft
Engine: 466ci
Rated Cap: 90
After breaking a few screw tips. Even when using cutting oil, I found it better to drill, passing through the wood pilot holes, into steel rib using an 3/8" oiled cobalt bit, prior to driving in the tek screws.



The screws do well at self-tapping, only okay at self drilling. A partner w/ a sized length of 2x4 to hold the wood tight against the ceiling rib is required. Clamps are ok, but tough to align.


Make sure to size your screws to the thickness of your framing framing material.
__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Old 06-19-2022, 01:27 PM   #4
Bus Crazy
 
DeMac's Avatar
 
Join Date: Oct 2020
Location: Florida
Posts: 1,570
Coachwork: Integrated Coach Corp.
Chassis: RE-300 42ft
Engine: 466ci
Rated Cap: 90
No jig or Craig tool

I don't have a Craig tool. I've had intentions of buying one for years. Maybe the price helps me forget.


My butt joints were completed while clamped. Predrilled (5/64"?), then toe-nailed using two 2-1/4" deck screws (also by Tek)


Blindside is toenailed, as well.
__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Old 06-19-2022, 01:39 PM   #5
Bus Crazy
 
DeMac's Avatar
 
Join Date: Oct 2020
Location: Florida
Posts: 1,570
Coachwork: Integrated Coach Corp.
Chassis: RE-300 42ft
Engine: 466ci
Rated Cap: 90
Member Spacing

The center four framing members (three spaces) are 16"oc. The outside two are each spaced at 12"oc





I used string to find the center and measured off the string to each stud. Originally, I was transferring the string center onto the ribs with sharpie. Seemed harder to see the black.





__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Old 06-19-2022, 01:50 PM   #6
Bus Crazy
 
DeMac's Avatar
 
Join Date: Oct 2020
Location: Florida
Posts: 1,570
Coachwork: Integrated Coach Corp.
Chassis: RE-300 42ft
Engine: 466ci
Rated Cap: 90
Center Six Feet

Center Six Feet complete. C-clamp still in place.



(where am I standing)
__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Old 06-19-2022, 01:52 PM   #7
Bus Crazy
 
DeMac's Avatar
 
Join Date: Oct 2020
Location: Florida
Posts: 1,570
Coachwork: Integrated Coach Corp.
Chassis: RE-300 42ft
Engine: 466ci
Rated Cap: 90
Sliding Box Brackets



These telescopic brackets, with adjustable depth, are perfect for suspending mechanicals within the spray foam. (electric/data boxes & conduit, a/c condenser lines, pex, pvc & copper plumbing, propane gas, stereo speakers, etc)

Sliding Box Brackets are manufactured by nVent-Caddy, Erico, HoldRite, & others. They're available at electric supply, plumbing supply shops & big box stores, too.


Attached to & touching wood only, zero conduction. This is a 1.5" deep lighting box, same as the framing. With the 1.5" rib exposed, this allows for total of 3" spray in insulation. Ceiling down to 6ft, 4-1/2" already.
__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Old 06-19-2022, 02:06 PM   #8
Bus Crazy
 
DeMac's Avatar
 
Join Date: Oct 2020
Location: Florida
Posts: 1,570
Coachwork: Integrated Coach Corp.
Chassis: RE-300 42ft
Engine: 466ci
Rated Cap: 90
Box Location, Alignment & Spacing

I never assume the wall is straight, floor level, or ceiling flat. Construction is string used for accurate & speedy box alignment.



The lighting boxes are spaced about 4 ft apart. Each centered and aligned over a particular work space. None are near the ribs, by design.

__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Old 06-19-2022, 02:16 PM   #9
Bus Crazy
 
DeMac's Avatar
 
Join Date: Oct 2020
Location: Florida
Posts: 1,570
Coachwork: Integrated Coach Corp.
Chassis: RE-300 42ft
Engine: 466ci
Rated Cap: 90
Wire Selection



12/2 Solid Copper MC w/ Steel Armor & Polypropylene Wrap. 250ft / $175, red anti-shorts included. Available at Electric Supply Shops (big box stores typically carry Aluminum armor, aka: Armorlite).

12/2 is used throughout for 120v/20A circuits such as receptacles, small appliances & lighting.

Our bus roofs are very hot, increasing resistance. I use 20A rated wire but will de-rate the overhead circuits with 15A overcurrent protection devices. Both 20A rooftop AC circuits utilize 10/2, rated at 30A.
__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Old 06-19-2022, 02:29 PM   #10
Bus Crazy
 
DeMac's Avatar
 
Join Date: Oct 2020
Location: Florida
Posts: 1,570
Coachwork: Integrated Coach Corp.
Chassis: RE-300 42ft
Engine: 466ci
Rated Cap: 90
Boxes then Holes

Before we open the wire roll, I walk though with a drill, pulling an imaginary wire from box to box & drilling holes where they're needed.


Metal in the eye is no joke. Wear glasses.


For a tight fitting 7/8" bushing, I use a 1/2" hole-saw, then usinh a step bit / unibit I ream it to 13/16". Use lube. Test fit bushing until it goes in. (Gudentiche.)


Trade size half inch. Actual size 13/16"od, designed for 7/8" hole


Cable protection. Snap-in bushing aka push-in bushing. (Adding another hole.)




Yes, that's cutting oil dripping. I also test fitment as I ream. Very tight with locking clips. If it were not so tight, I'd use adheasive.
__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Old 06-19-2022, 03:06 PM   #11
Bus Crazy
 
DeMac's Avatar
 
Join Date: Oct 2020
Location: Florida
Posts: 1,570
Coachwork: Integrated Coach Corp.
Chassis: RE-300 42ft
Engine: 466ci
Rated Cap: 90
Cable Straps & Protection

NEC 300.4 Protection against physical damage
(For Non-Metalic Sheathed Cable - NMC)
(d) ...cable or raceway shall be installed and supported so that the nearest outside surface of the cable or raceway is not less than 1-1/4 in. (31.8 mm) from the nearest edge of the framing member where nails or screws are likely to penetrate.

Please reference the NEC 300-4



The cable is supported using CS8-12 cable straps (by Erico, Nvent, Caddy) to hold the cable away from the stud and mid-depth into the sprayfoam.




12/2 Solid Copper MC w/ Steel Armor (not Armorlite) is quite stiff, aiding bends when hand forming a gap as I cross the steel ribs.


Zero metal to rib/shell contact. No brackets overlapping rib screws. Nothing flopping around nor pulled taunt. Redundant strapping and cable ties.

Note: RV walls, ceilings, & floors are too thin to use NMC & still adhear to the minimum requirements of residential construction. RV exceptions are there for the NRVIA inspector.

(...more to come later... )
__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Old 06-19-2022, 10:20 PM   #12
Bus Crazy
 
DeMac's Avatar
 
Join Date: Oct 2020
Location: Florida
Posts: 1,570
Coachwork: Integrated Coach Corp.
Chassis: RE-300 42ft
Engine: 466ci
Rated Cap: 90
Forward Lighting


120v stair/egress lighting, front ac circuits & switchlegs. Also, routed local dc terminations to this access point.


Forward bulkhead: Strapped both existing dc wirelooms & new ac cable. Secured to framing using Mounting-Head Cable-Ties. All terminations routed to either (L) or (R) access points.


Wide view. Additional lighting boxes to the right & left. At the top of the photo, you can see the box for the front rooftop AC (future use).
__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Old 06-19-2022, 10:37 PM   #13
Bus Crazy
 
DeMac's Avatar
 
Join Date: Oct 2020
Location: Florida
Posts: 1,570
Coachwork: Integrated Coach Corp.
Chassis: RE-300 42ft
Engine: 466ci
Rated Cap: 90
Hatch Bezel and Framing Thickness


Rearward view of the same front, rooftop ac box in the previous post.

Side Note:
Even after adding 1-1/2" of framing, there's still about 3/8" of overlap between the inner & outer trim pieces of the hatch. I was skeptical beforehand.



(front facing)
Here again the mc wire, where crossing perpendicular over top, is screwed to the framing members using Mounting-Head Cable Ties
__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Old 06-19-2022, 10:53 PM   #14
Bus Crazy
 
DeMac's Avatar
 
Join Date: Oct 2020
Location: Florida
Posts: 1,570
Coachwork: Integrated Coach Corp.
Chassis: RE-300 42ft
Engine: 466ci
Rated Cap: 90
Installation Details


*1/2" Snap-in bushing
*MC wire protectors, anti-shorts


Mechanical mc connector, anti-short and ground screw.


I prefer hand drivers when securing cable connectors. Power drivers inevitably guillotine the cable & cause hidden shorts.
__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Old 06-19-2022, 11:02 PM   #15
Bus Crazy
 
DeMac's Avatar
 
Join Date: Oct 2020
Location: Florida
Posts: 1,570
Coachwork: Integrated Coach Corp.
Chassis: RE-300 42ft
Engine: 466ci
Rated Cap: 90
More Lighting


Staggered lighting over dual countertops, same equidistant spacing on both sides. Tight spacing between mc supports, redundantly secured.



Provide ample cable length for alterations in lighting layout & fixture product selection by forming wide radius bends and supporting mc to the adjacent rafter, mounting-head cable ties over the top.


Center of the bus, main panel location and five switchlegs (two in 12/3) all in one stud bay (wall cavity)
__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Old 06-19-2022, 11:14 PM   #16
Bus Crazy
 
DeMac's Avatar
 
Join Date: Oct 2020
Location: Florida
Posts: 1,570
Coachwork: Integrated Coach Corp.
Chassis: RE-300 42ft
Engine: 466ci
Rated Cap: 90
Rear Lighting & Rooftop AC


I used 10/2 mc (30A rated) for the roofrop heat, a/c, dehumidifier.


Note the cable arching under the ribs.




Rear bench & emergency egress lighting.
__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Old 06-19-2022, 11:36 PM   #17
Skoolie
 
Join Date: May 2017
Location: Gulfport, MS
Posts: 154
Year: 2000
Coachwork: Bluebird All American Re
Engine: Cat 3126
Nice work! (That's an understatement) I appreciate the craftsmanship and attention to detail where safety is concerned. Last thing any of us needs to do is burn down a rig because of shotty electrical work. You have already helped me out with a wall framing issue recently and I will be starting on my ceiling next weekend so this thread gets an automatic subscribe from me. Thanks for taking the time to document and post with such great detail.
bridg73988 is offline   Reply With Quote
Old 06-20-2022, 10:39 AM   #18
Bus Crazy
 
Join Date: Apr 2020
Location: Northern California (Sacramento)
Posts: 1,435
Year: 1999
Coachwork: El Dorado Fiberglass
Chassis: Ford E450
Engine: V10 Gas
Beautiful exposition. This is how we should all work.
Rucker is offline   Reply With Quote
Old 06-20-2022, 10:48 AM   #19
Bus Crazy
 
TheHubbardBus's Avatar
 
Join Date: Apr 2019
Location: SW USA
Posts: 2,064
Year: 2003
Coachwork: IC / Amtran
Chassis: CE300
Engine: International T444e
Rated Cap: 23
Great stuff, DeMac! Thanks for sharing.
__________________
Go away. 'Baitin.

Our Build: Mr. Beefy
TheHubbardBus is offline   Reply With Quote
Old 06-20-2022, 07:59 PM   #20
Bus Crazy
 
DeMac's Avatar
 
Join Date: Oct 2020
Location: Florida
Posts: 1,570
Coachwork: Integrated Coach Corp.
Chassis: RE-300 42ft
Engine: 466ci
Rated Cap: 90
Thank you, all. I appreciate each of your feedback.
__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Reply

Tags
120v electric, electric panel, electrical wiring, fur strips, shore power


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -5. The time now is 04:28 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.