Quote:
Originally Posted by Smitty
Though you got it solved....I just used a jumper (from one lug to the other) to make both buss bars hot.
Smitty
|
With only two breakers, another solution is to just connect one lug making one of the two busses hot, and install the two breakers opposite each other on the same hot buss. Fill in the box with alternate breakers and blanks going down each side, such as:
1 - hot
3 - not used
5 - hot
7 - not used
etc.
The even numbered breakers in the right column will generally be on the same buss as the odd ones directly to their left
If you want to be to code, connect all the neutrals to a buss insulated from the box, and do not tie the neutrals to the ground system. Put the grounds on a separate buss tied to the panel case. The power source (campground, genset) should make the neutral bond connection for you.