RV Breaker Panel vs Home Breaker Panel

I am researching around the internet and notice that most conversions seem to be using a 120v breaker panel that is combined with 12v, designed specifically for RVs. I bought a 120v breaker panel from home depot designed for homes and am intending to buy a separate 12v fuse board for everything else, primarily because nearly everything in my conversion is going to be 120v except those things that require 12.

My questions are, is it illegal to use a house breaker panel? Is there any reason I should consider a panel designed for RVs? Any recommendations?

karlw is offline   Reply With Quote
Old 05-19-2016, 01:51 AM   #2
Skoolie
 
Join Date: Mar 2010
Location: Texas
Posts: 218
Year: 1997
Coachwork: AmTran
Chassis: Genesis
Engine: DT466
Rated Cap: 84
My understanding is that such designs are usually for size constraints or convenience rather than anything to do with legality.
Timelord is offline   Reply With Quote
Old 05-19-2016, 06:25 AM   #3
Bus Nut
 
superdave's Avatar
 
Join Date: Mar 2015
Location: hills of sw virginia
Posts: 889
Year: 1996
Chassis: thomas
Engine: 8.3 cummins
Rated Cap: 11 window
there will be a little green screw with that breaker box, DO NOT bond the neutral with the ground. the ground bus bar should be bonded to the frame. wire everything as you would a house. if you have a on board genny the nuetral and ground are bonded at the genny from the factory, on most models.
__________________
living in a bus down by the river.
my build pics
https://www.skoolie.net/forums/membe...albums942.html
superdave is offline   Reply With Quote
Old 05-19-2016, 06:55 AM   #4
Bus Geek
 
EastCoastCB's Avatar
 
Join Date: Sep 2014
Location: Eustis FLORIDA
Posts: 23,764
Year: 1999
Coachwork: Thomas
Chassis: Freighliner FS65
Engine: Cat 3126
Rated Cap: 15
Quote:
Originally Posted by superdave View Post
there will be a little green screw with that breaker box, DO NOT bond the neutral with the ground. the ground bus bar should be bonded to the frame. wire everything as you would a house. if you have a on board genny the nuetral and ground are bonded at the genny from the factory, on most models.
Love the avatar!!
EastCoastCB is offline   Reply With Quote
Old 05-19-2016, 07:15 AM   #5
Skoolie
 
Arvik's Avatar
 
Join Date: Dec 2015
Location: onboard
Posts: 235
Year: 97
Coachwork: Thomas
Chassis: BadMuthaFuka
Engine: Cummins 5.9
Rated Cap: All of us
just finished wiring mine this am. i went with the 12v and 110 combined . this makes it possible to safe space and have all wires close.
no legalities involved that i know of.
if you gonna have your battery bank near the panel then just get the combined one to save yourself the hassel, if it not close to bank then you will want the 12v panel seperate any way in order to keep runs short. plus the combined looks very clean and easy access when finished. its all about space,
here is the one i went with http://www.amazon.com/WFCO-50-Servic...ilpage_o09_s00
__________________
The road is crazy.
Be safe
Arvik is offline   Reply With Quote
Old 05-19-2016, 08:01 AM   #6
Bus Crazy
 
turf's Avatar
 
Join Date: Apr 2013
Location: Colorado
Posts: 2,356
Year: 1993
Coachwork: bluebird
Engine: 5.9 Cummins, Allison AT1545
Rated Cap: 2
i have the WFCO box and i wish i got something a bit better.


check out blue sea marine for some nice high quality DC power distribution components.

https://www.bluesea.com/

good luck
__________________
.
Turfmobile Build Thread
turf is offline   Reply With Quote
Old 05-19-2016, 08:08 AM   #7
Bus Nut
 
Join Date: Feb 2014
Location: The Valley - Arizona
Posts: 644
Year: 1999
Coachwork: Thomas
Chassis: Freight-shaker (Freightliner)
Engine: Cat 3126b 250 HP
Rated Cap: Only 1 seat
I am doing the 120V house breaker as well. I am running a separate line from the batteries directly to an automotive fuse panel with an inline shut off for 12v things. and then all my 12V will have fuses to protect them.
Docsgsxr is offline   Reply With Quote
Old 05-19-2016, 09:24 AM   #8
Bus Crazy
 
2kool4skool's Avatar
 
Join Date: Oct 2015
Location: Spring Valley AZ
Posts: 1,343
Year: 2000
Coachwork: Bluebird
Engine: 5.9 Cummins
Rated Cap: 2 elderly children, 1 cat
120v house panel and separate 12v with auto fuses. I use a 15a smart charger for the 4 100ah batts...does double duty if I need something else charged. 200w solar kicker too.

__________________
Don, Mary and Spooky the cat.
2kool4skool is online now   Reply With Quote
Old 05-19-2016, 12:39 PM   #9
Skoolie
 
Arvik's Avatar
 
Join Date: Dec 2015
Location: onboard
Posts: 235
Year: 97
Coachwork: Thomas
Chassis: BadMuthaFuka
Engine: Cummins 5.9
Rated Cap: All of us
on side note, i ground a nice shiny spot on the rail the seats were attached to along bottom of wall to use for ground. good spot , bad spot?? isn't that technically the chasis? or should i ground elsewhere?
__________________
The road is crazy.
Be safe
Arvik is offline   Reply With Quote
Old 05-19-2016, 02:51 PM   #10
Bus Crazy
 
Join Date: Feb 2012
Location: Salt Lake City Utah
Posts: 1,635
Year: 2000
Chassis: Blue Bird
Engine: ISC 8.3
Depends on what's being grounded, or in other words, how good the connection needs to be. Remember you're building an electric circuit. I'll suppose you're talking about "ground" as in the negative battery return. People are pretty good at seeing the positive side of the circuit: the battery post, clamp, heavy wire with lugs on both ends, fuse box, smaller wire going out to the load. The negative/return half of the circuit tends to be invisible. From the load you might have a short wire, a ring terminal, a sheet metal screw holding it to some body panel, a combination of sheet metal screws, bolts, and rivets holding a series of body panels together, somewhere a braid or heavy wire with lugs and bolts or screws connecting a body panel down to the frame, and finally a heavy wire with lugs and bolts connecting the frame back to the battery.

People forget all about those connections between the body components; they think of the chassis/body as a single unit. Electrically it isn't, though: anything that isn't welded together has a connection that may become loose, dirty, etc. When somebody is being really careful, perhaps because they're installing a radio transceiver or audio equipment, it's sometimes necessary to actually install jumpers between everything that isn't welded because though the mechanical connection is reliable, the electrical connection may not be. Common parts include door panels, the hood, fender panels that aren't welded, etc.

A shiny spot on the chair rail "could" be a good place for a ground.
family wagon is offline   Reply With Quote
Old 05-19-2016, 04:14 PM   #11
Bus Geek
 
Join Date: May 2009
Location: Columbus Ohio
Posts: 18,753
Year: 1991
Coachwork: Carpenter
Chassis: International 3800
Engine: DTA360 / MT643
Rated Cap: 7 Row Handicap
so I have a question... isnt it a bad scene to be grounding your 110 volt panels to the same frame that alot of your 12 volt stuff is grounded to? shouldnt you be running grounds to each appliance / receptacle.. and then WIRING a ground to the Generator or to the Shore power connection? and leave the Bus frame for the 12 volt stuff?
-Christopher
cadillackid is offline   Reply With Quote
Old 05-19-2016, 08:17 PM   #12
Bus Crazy
 
Join Date: Feb 2012
Location: Salt Lake City Utah
Posts: 1,635
Year: 2000
Chassis: Blue Bird
Engine: ISC 8.3
Nope. If there's going to be an ac system installed in the bus, just like any other metal building construction, the safety ground should be connected to the bus body. Without that connection devices like ground fault interrupters and over-current circuit breakers can fail to operate, ie fail to clear some types of faults by automatically disconnecting the power.

Incidentally some inverters (specifically the Xantrex PROwatt model I have) instruct that their cabinet, which is connected to the ground pin on the built-in 120v receptacles, should be connected to the dc negative/ground. When I bench tested that inverter I learned the reason for this: left unconnected its chassis floats at 60v relative to the dc input. When an unsuspecting person rests one hand on the chassis and touches either battery connection with the other hand, it results in a pretty good shock!
family wagon is offline   Reply With Quote
Old 05-19-2016, 09:10 PM   #13
Bus Geek
 
Robin97396's Avatar
 
Join Date: Feb 2016
Location: Willamina, Oregon
Posts: 6,409
Coachwork: 97 Bluebird TC1000 5.9
That sounds better than a car alarm. The old guys used to do that with model T coils to keep people from sitting on their car hoods.
Robin97396 is offline   Reply With Quote
Old 05-19-2016, 09:37 PM   #14
New Member
 
Join Date: Jan 2016
Posts: 4
We've got the RV type, and it works pretty well. It's got a built in 3-stage charger that's completely automatic. We really don't even think about it. The biggest drawback is that it would be nice to have a few more 120v. circuits. We've got it maxed out with double breakers. That takes care of everything that we've got, but if we ever decide to add a circuit we're pretty much out of luck. I guess either way has plusses and minuses.
dadelay is offline   Reply With Quote
Old 05-25-2016, 06:42 PM   #15
Skoolie
 
Join Date: Feb 2015
Location: Miami
Posts: 172
Year: 1998
Coachwork: Thomas
Chassis: MVP
Engine: CAT 3116
Rated Cap: 84
Quote:
Originally Posted by family wagon View Post
Nope. If there's going to be an ac system installed in the bus, just like any other metal building construction, the safety ground should be connected to the bus body. Without that connection devices like ground fault interrupters and over-current circuit breakers can fail to operate, ie fail to clear some types of faults by automatically disconnecting the power.
OK, now I'm officially confused! I was under the impression that the grounding was done via the incoming shore power and not to the bus frame. I just bought a Progressive Dynamics 4560 All in One center, and the installation guide that came with it (http://www.progressivedyn.com/pdfs/110030%20English.pdf ) shows the panel's ground bar being wired to the incoming ground connection. It does not show a ground connection to the bus body?

Another reason for my confusion is that grounding it to the bus would not seem to accomplish much as the bus itself is isolated from the ground by the rubber tires..
Piersg is offline   Reply With Quote
Old 05-25-2016, 06:48 PM   #16
Skoolie
 
Arvik's Avatar
 
Join Date: Dec 2015
Location: onboard
Posts: 235
Year: 97
Coachwork: Thomas
Chassis: BadMuthaFuka
Engine: Cummins 5.9
Rated Cap: All of us
Quote:
Originally Posted by Piersg View Post
OK, now I'm officially confused! I was under the impression that the grounding was done via the incoming shore power and not to the bus frame. I just bought a Progressive Dynamics 4560 All in One center, and the installation guide that came with it (http://www.progressivedyn.com/pdfs/110030%20English.pdf ) shows the panel's ground bar being wired to the incoming ground connection. It does not show a ground connection to the bus body?

Another reason for my confusion is that grounding it to the bus would not seem to accomplish much as the bus itself is isolated from the ground by the rubber tires..
you still need to be thinking about a ground for when you arent plugged into shore. ie only running off your batteries. it does show it in your manual, your hardware has the "optional chasis ground in it" your main breaker hold down screw goes right over it. i think
__________________
The road is crazy.
Be safe
Arvik is offline   Reply With Quote
Old 05-25-2016, 07:00 PM   #17
Bus Crazy
 
Join Date: Feb 2012
Location: Salt Lake City Utah
Posts: 1,635
Year: 2000
Chassis: Blue Bird
Engine: ISC 8.3
Quote:
Originally Posted by Piersg View Post
OK, now I'm officially confused! I was under the impression that the grounding was done via the incoming shore power and not to the bus frame. I just bought a Progressive Dynamics 4560 All in One center, and the installation guide that came with it (http://www.progressivedyn.com/pdfs/110030%20English.pdf ) shows the panel's ground bar being wired to the incoming ground connection. It does not show a ground connection to the bus body?
Right. Well, kind of. The ground-to-neutral "bond" connection is done for you in the shore power system. I'm not in a position to speak for Progressive, but I could at least speculate they don't mention connecting the panel's ground bar to the vehicle body because they're working in a world where RVs are made of wood, not metal. Of course it wouldn't make any sense to wire a wood body to the ground bar.

Quote:
Originally Posted by Piersg View Post
Another reason for my confusion is that grounding it to the bus would not seem to accomplish much as the bus itself is isolated from the ground by the rubber tires..
That's part of the reason why it's important. Though even if it sat on steel wheels, or had metal stabilizer jacks down, it would still be a poor electrical connection to earth.

Have you seen Mike Sokol's No Shock Zone writings? They're pretty good. His part IV addresses "Hot Skin" and part VII addresses "GFCI Theory"; both are relevant to why the bus body should be well grounded.
family wagon is offline   Reply With Quote
Old 05-25-2016, 07:02 PM   #18
Skoolie
 
Join Date: Feb 2015
Location: Miami
Posts: 172
Year: 1998
Coachwork: Thomas
Chassis: MVP
Engine: CAT 3116
Rated Cap: 84
Quote:
Originally Posted by jester View Post
you still need to be thinking about a ground for when you arent plugged into shore. ie only running off your batteries. it does show it in your manual, your hardware has the chasis ground in it. i think
The DC side is grounded to the chasis, I understand that, and I can see an inverter being grounded if needed, but I think the panel itself is not grounded.
Piersg is offline   Reply With Quote
Old 05-25-2016, 07:15 PM   #19
Skoolie
 
Join Date: Feb 2015
Location: Miami
Posts: 172
Year: 1998
Coachwork: Thomas
Chassis: MVP
Engine: CAT 3116
Rated Cap: 84
Quote:
Originally Posted by family wagon View Post
Right. Well, kind of. The ground-to-neutral "bond" connection is done for you in the shore power system. I'm not in a position to speak for Progressive, but I could at least speculate they don't mention connecting the panel's ground bar to the vehicle body because they're working in a world where RVs are made of wood, not metal. Of course it wouldn't make any sense to wire a wood body to the ground bar.


That's part of the reason why it's important. Though even if it sat on steel wheels, or had metal stabilizer jacks down, it would still be a poor electrical connection to earth.

Have you seen Mike Sokol's No Shock Zone writings? They're pretty good. His part IV addresses "Hot Skin" and part VII addresses "GFCI Theory"; both are relevant to why the bus body should be well grounded.
OK, just read through this thread (http://www.skoolie.net/forums/f10/ho...-ac-448-6.html ) again, and downloaded no shock zone. Confusion is cleared up.
Piersg is offline   Reply With Quote
Old 05-25-2016, 08:15 PM   #20
Bus Geek
 
ol trunt's Avatar
 
Join Date: Apr 2012
Location: So Cal
Posts: 3,227
Year: 1935
Coachwork: Superior
Chassis: Chevy
Engine: 317 ci/tid / Isuzu
The no shock zone should be mandatory reading for all us bus nuts!!!!!!

If you are using a portable generator like Honda or Yamaha you will need to change their floating grounds so that they ground back to themselves. Many portable generators have a ground lug on the control panel that the mfg suggests you wire to a grounding rod---how likely is that going to be? You can find a listing of generators with floating grounds and how to make their grounds go back to the generator rather than a ground rod. With a floating generator ground, it is possible for the "skin" of the bus to become hot (electrified). Under those conditions, should you happen to step out of your bus onto wet ground while you are still, say, hanging onto the step rail, you get to be the ground----a shocking (and potentially deadly) experience. Jack
ol trunt is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -5. The time now is 09:18 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.