Post 8s/24v battery balancing

Greetings all!

I have 4 x 8s/24v batteries that I put together, with each set of 8 cells attached to a BMS. I accidentally tripped one of the battery breakers manually (i.e. it did not trip due to an electrical fault) when it was depleted.

Now, it appears that at least one of the batteries is unbalanced with the rest, which is causing my inverters to shut down as they sense low voltage. I spoke with the inverter rep and he recommended ordering 5 48v/4 cell balancers and running daisy chaining them together to balance all the cells.

But, in addition to being expensive, it seems like the BMS already balances each cell it is connected too, so shouldn't I just be able to balance the batteries as a unit? If so, does anyone have a link or recommendation on what to use for that? I can only seem to find balancers designed for 12v batteries.

Any other suggestions or recommendations are appreciated!

Jeremy

jjaj823 is offline   Reply With Quote
Old 08-24-2021, 11:59 AM   #2
Bus Nut
 
Join Date: Sep 2017
Location: Cerrillos, NM
Posts: 393
Year: 2002
Coachwork: Amtran
Chassis: Front Engine
Engine: DT466E
Rated Cap: 72
I could be wrong for sure but my approach would be to take the low bank out of the situation and charge up the other 3, then connect only the 4th bank and charge that up until similarly full to the others and reconnect the whole mess at that point.

There may be some issue with having 4 separate batteries as opposed to a single 4p8s battery. From what I understand (again, could be wrong) these batteries like to be connected in parallel first then series so that you don’t end up in this kinda circumstance.
rffffffff is offline   Reply With Quote
Old 08-24-2021, 02:36 PM   #3
Bus Geek
 
Join Date: Nov 2016
Posts: 2,775
Use balancing gear that accurately displays the individual cell voltages.

Then get one set of cells balanced at a time.

When all are good then reassemble the bank as a whole.
john61ct is offline   Reply With Quote
Old 08-24-2021, 03:23 PM   #4
Bus Geek
 
Join Date: May 2014
Location: West Ohio
Posts: 3,712
Year: 1984
Coachwork: Bluebird
Chassis: International 1753
Engine: 6.9 International
Rated Cap: 65
I'd separate the system and charge each battery individually. Then reconnect them into your system. What BMS do you have?
__________________
My build: The Silver Bullet https://www.skoolie.net/forums/f11/p...llet-9266.html
Booyah45828 is offline   Reply With Quote
Old 08-24-2021, 05:43 PM   #5
Bus Nut
 
Bert06840's Avatar
 
Join Date: Mar 2021
Location: Connecticut
Posts: 638
Year: 2009
Coachwork: Gillig
Chassis: G27E102
Engine: Cummins ISL 280
Rated Cap: 26,000 lbs
Quote:
Originally Posted by jjaj823 View Post
I have 4 x 8s/24v batteries that I put together, with each set of 8 cells attached to a BMS. I accidentally tripped one of the battery breakers manually (i.e. it did not trip due to an electrical fault) when it was depleted.
I hope you don't have a circuit breaker between your cells and your BMSes. You shouldn't, and if you do, you may have deep discharged one cell.

Also, how long did you store your packs in a discharged state?

Have you measured the cell voltages of each of the cells in each of the packs? That will give you much of the information you need to make further determinations.

Quote:
Originally Posted by jjaj823 View Post
Now, it appears that at least one of the batteries is unbalanced with the rest, which is causing my inverters to shut down as they sense low voltage.
So you have four battery packs, each made out of 8 series connected cells, each with their own BMS. And these four packs are wired up in parallel onto a 24V bus. Is that correct?

If your inverters shut down in that configuration, you have FOUR bad packs, or something else is going on. I'm assuming here that you don't draw that much current that you need four parallel connected packs to supply the current.

Quote:
Originally Posted by jjaj823 View Post
I spoke with the inverter rep and he recommended ordering 5 48v/4 cell balancers and running daisy chaining them together to balance all the cells.
That is terrible advice. You can have vastly different cells in each of the packs. Only the cells INSIDE one pack, when connected in series, need to be similar. He's trying to sell you stuff you don't need.

Quote:
Originally Posted by jjaj823 View Post
But, in addition to being expensive, it seems like the BMS already balances each cell it is connected
Yes, but the balancing current of BMSes is often in the sub 100mA, which is adequate for a healthy pack, but not necessarily for one that is out of whack.

, [QUOTE=jjaj823;450557]You don't need any of that. You just need a 3.5V power supply with current limiting. Attach the supply to each cell individually, until it stops pulling current.

Something like this if you don't have it already: https://www.amazon.com/dp/B08HQ92R8C...NsaWNrPXRydWU=

But before you do that, measure first. Always measure first.

Quote:
Originally Posted by jjaj823 View Post
If so, does anyone have a link or recommendation on what to use for that? I can only seem to find balancers designed for 12v batteries.
There are plenty of 8S balancers out there. Like this one https://www.amazon.com/gp/product/B0...73ZEKLGH&psc=1 but I have never had the need for one.

But yeah, make sure you're not being BSed, because you do not need identical packs to parallel. I have a 130Ah and a 200Ah pack in parallel and they play nice just fine.
Bert06840 is offline   Reply With Quote
Old 08-26-2021, 11:00 PM   #6
Skoolie
 
Join Date: Mar 2020
Location: Anywhere we can park (currently PA)
Posts: 134
Year: 2004
Coachwork: International
Chassis: RE300
Engine: DT466E
Rated Cap: 76
Thumbs up Thanks!

Thanks everyone for the responses!

I think I'll go ahead and remove each pack individually, test/balance if needed and then reassemble & reinstall.

Anyone have any ideas on how to check if the BMS is OK?
jjaj823 is offline   Reply With Quote
Old 08-26-2021, 11:35 PM   #7
Bus Nut
 
Bert06840's Avatar
 
Join Date: Mar 2021
Location: Connecticut
Posts: 638
Year: 2009
Coachwork: Gillig
Chassis: G27E102
Engine: Cummins ISL 280
Rated Cap: 26,000 lbs
Measure voltages, it’ll become immediately clear if one is out of line.

And does your bms not have a user interface like so:

Click image for larger version

Name:	IMG_3135.jpg
Views:	14
Size:	218.5 KB
ID:	60725
Bert06840 is offline   Reply With Quote
Old 08-27-2021, 12:00 AM   #8
Skoolie
 
Join Date: Mar 2020
Location: Anywhere we can park (currently PA)
Posts: 134
Year: 2004
Coachwork: International
Chassis: RE300
Engine: DT466E
Rated Cap: 76
My BMS definitely does NOT have an interface like that!

What are you using?
jjaj823 is offline   Reply With Quote
Old 08-27-2021, 10:33 AM   #9
Skoolie
 
Join Date: Mar 2020
Location: Anywhere we can park (currently PA)
Posts: 134
Year: 2004
Coachwork: International
Chassis: RE300
Engine: DT466E
Rated Cap: 76
Follow up question also:

Would I be better* off reconfiguring into something like 2 x 2p/s or 1 4p/8s battery instead?

*= with the understanding that "better" can be subjective...
jjaj823 is offline   Reply With Quote
Old 08-27-2021, 10:46 AM   #10
Bus Crazy
 
Join Date: Apr 2020
Location: Northern California (Sacramento)
Posts: 1,437
Year: 1999
Coachwork: El Dorado Fiberglass
Chassis: Ford E450
Engine: V10 Gas
Quote:
Originally Posted by jjaj823 View Post
My BMS definitely does NOT have an interface like that!

What are you using?
I'm using a Daly 250A unit. Yes, it does have cell balancing but I leave that function to the cheap capacitor-type active cell balancing PCBs. The BMS theoretically balances but as mentioned, only at very low current, and even then only when cells are almost fully charged. Will Prowse has a video on the performance of the Daly. I consider the Daly nothing more than a glorified circuit breaker. It has temp monitoring, but apparently that doesn't work correctly, again, per Prowse.

I've wired up the cheap balancer, which is actually really effective, but I unplugged it after initial balancing and so far the cells have been maintained by the Daly.
Rucker is offline   Reply With Quote
Old 08-27-2021, 12:21 PM   #11
Bus Nut
 
Join Date: Sep 2017
Location: Cerrillos, NM
Posts: 393
Year: 2002
Coachwork: Amtran
Chassis: Front Engine
Engine: DT466E
Rated Cap: 72
Quote:
Originally Posted by jjaj823 View Post
Follow up question also:

Would I be better* off reconfiguring into something like 2 x 2p/s or 1 4p/8s battery instead?

*= with the understanding that "better" can be subjective...

This is my understanding. Cells like this prefer to be paralleled at the cell level instead of pack level like you have currently. Do a little more digging but it’ll solve some of your balancing issues cause it’s only one battery at that point.
rffffffff is offline   Reply With Quote
Old 08-27-2021, 01:51 PM   #12
Bus Nut
 
Bert06840's Avatar
 
Join Date: Mar 2021
Location: Connecticut
Posts: 638
Year: 2009
Coachwork: Gillig
Chassis: G27E102
Engine: Cummins ISL 280
Rated Cap: 26,000 lbs
Quote:
Originally Posted by jjaj823 View Post
Would I be better* off reconfiguring into something like 2 x 2p/s or 1 4p/8s battery instead?
The short answer is a tiny, reserved maybe, with asterisks and disclaimers.
A more sensible answer is: almost likely not.

If you parallel multi-kilowatt-hour packs on cell level, you get the potential for large currents. That comes with a series of issues, most notably risk for high contact resistance (in this context: milli-ohms), which causes fires. The plating on the nut, washer and lug, the torque, the material of bus bars start to become very significant. For currents up to, say, 100A you get away with "nah feels about tight". In the 300-500A range you do not any more.

Also, there isn't much to be gained. I can think of only one - really terrible - scenario. Say you bought 16 cells to make a 24V pack, but they test all over the place. Say five come in 80Ah, four at 100Ah, and seven at 30Ah. Normally you would make only strings of similar capacities. But if you don't have enough cells from each capacity bucket, you may take for example four 30Ah cells and four 80Ah cells, and parallel them up in 80Ah-30Ah pairs, so you end up with four de facto 110Ah cells. Then, you could make a string of four 110Ah duo-cells, and four regular 100Ah cells, and you you could access 100Ah of the total pack. You'd have a 80Ah cell and three 30Ah cells left over, but at least there is that.

Now, that is a terrible idea for many reasons, and cells that are so far gone have no business being anywhere near humans. So don't do this.

It is much wiser to have multiple smaller current pack paralleled after the BMS, all fused individually. When things go haywire, you have the BMSes and the fuses to CYA in at least some horrible scenarios.

Even if you had a series of identical cells, bus bars the size of your arm, copper nuts, and a calibrated torque wrench, you still want to avoid paralleling at that level. If nothing else you are going to need a very large BMS, and there are very few of them for the reasons mentioned above. Up to say, 100A they are a dime a dozen, figuratively speaking.
Bert06840 is offline   Reply With Quote
Old 08-29-2021, 03:57 PM   #13
Skoolie
 
Join Date: Mar 2020
Location: Anywhere we can park (currently PA)
Posts: 134
Year: 2004
Coachwork: International
Chassis: RE300
Engine: DT466E
Rated Cap: 76
Starting from the beginning

Whelp,

I decided to take the packs apart, balance everything and rebuild using the Overkill Solar BMSs. I chose them because they are at least sent from the US and are not much more than the Daly shipped directly from China.

Hopefully, performing a top balance and getting new BMSs that allow me to monitor at the cell level will solve my issues.

Thanks everyone for your input on this...it is very much appreciated!

Jeremy
jjaj823 is offline   Reply With Quote
Old 08-29-2021, 09:59 PM   #14
Bus Nut
 
Bert06840's Avatar
 
Join Date: Mar 2021
Location: Connecticut
Posts: 638
Year: 2009
Coachwork: Gillig
Chassis: G27E102
Engine: Cummins ISL 280
Rated Cap: 26,000 lbs
I also got one from overkill Solar. It is a regular Xiaoxiang, but it doesn’t matter. He supports his stuff, that’s worth the difference in price.

Ps those BMS work just fine.
Bert06840 is offline   Reply With Quote
Old 08-29-2021, 10:37 PM   #15
Skoolie
 
Join Date: Mar 2020
Location: Anywhere we can park (currently PA)
Posts: 134
Year: 2004
Coachwork: International
Chassis: RE300
Engine: DT466E
Rated Cap: 76
Quote:
Originally Posted by Bert06840 View Post
I also got one from overkill Solar. It is a regular Xiaoxiang, but it doesn’t matter. He supports his stuff, that’s worth the difference in price.

Ps those BMS work just fine.
Good to hear! Support was another reason I went with them. Glad to hear another good experience!

Jeremy
jjaj823 is offline   Reply With Quote
Old 09-01-2021, 06:05 PM   #16
Bus Nut
 
BusT's Avatar
 
Join Date: Jan 2019
Location: Houston
Posts: 336
Year: 2003
Engine: Dt466e
Rated Cap: 30,000
If you have 16 280ah cells could you make a pack of 8 using overkill solar 100amp bms and parallel that with another 8s pack that has a bms for 24v 560ah ?
That’s what I’m trying to do have my cells but alittle lost on the bms but did order two on Monday. Also purchased dc bench top charger and hoping to top balance pack in a 8s pack altogether .
BusT is offline   Reply With Quote
Old 09-01-2021, 06:23 PM   #17
Skoolie
 
Join Date: Mar 2020
Location: Anywhere we can park (currently PA)
Posts: 134
Year: 2004
Coachwork: International
Chassis: RE300
Engine: DT466E
Rated Cap: 76
Quote:
Originally Posted by BusT View Post
If you have 16 280ah cells could you make a pack of 8 using overkill solar 100amp bms and parallel that with another 8s pack that has a bms for 24v 560ah ?
That’s what I’m trying to do have my cells but alittle lost on the bms but did order two on Monday. Also purchased dc bench top charger and hoping to top balance pack in a 8s pack altogether .
Yes, you *could* technically do that.

However, you would be limited to 100a discharge current.

Just to give you an example, my 120AH cells have a max sustained discharge of 120A, and a surge higher than that for about 30 seconds or so.

If your electrical doesn't have a ton of DC draw, that might work for you. For me, I have serval high draw items where 100-150A is common for relatively short duration. I also have dual inverters in split phase providing 240v AC. For me, it made more sense to create 4x 8s packs, giving me a theoretical max current draw of 480A. I approximate that I will never exceed 225 though, so it gives me some room.

Basically, all that is to say you may be limiting yourself if you go with a 2p/8s pack instead of 2 x 8s packs.

Hope that helps a bit!

Jeremy
jjaj823 is offline   Reply With Quote
Old 09-01-2021, 06:28 PM   #18
Bus Nut
 
Join Date: Sep 2017
Location: Cerrillos, NM
Posts: 393
Year: 2002
Coachwork: Amtran
Chassis: Front Engine
Engine: DT466E
Rated Cap: 72
When you build a 2p8s pack you’re doubling the current capacity of the battery too so you can draw the same current as 2 x 8S packs. You have to make sure the bms and all the rest can handle that but the way you build it shouldn’t create any specific limitation one way or the other as long as all the bus bars etc are up to handling it.
rffffffff is offline   Reply With Quote
Old 09-01-2021, 10:38 PM   #19
Bus Nut
 
Bert06840's Avatar
 
Join Date: Mar 2021
Location: Connecticut
Posts: 638
Year: 2009
Coachwork: Gillig
Chassis: G27E102
Engine: Cummins ISL 280
Rated Cap: 26,000 lbs
Quote:
Originally Posted by jjaj823 View Post
Yes, you *could* technically do that.

However, you would be limited to 100a discharge current.

Just to give you an example, my 120AH cells have a max sustained discharge of 120A, and a surge higher than that for about 30 seconds or so.

If your electrical doesn't have a ton of DC draw, that might work for you. For me, I have serval high draw items where 100-150A is common for relatively short duration. I also have dual inverters in split phase providing 240v AC. For me, it made more sense to create 4x 8s packs, giving me a theoretical max current draw of 480A. I approximate that I will never exceed 225 though, so it gives me some room.

Basically, all that is to say you may be limiting yourself if you go with a 2p/8s pack instead of 2 x 8s packs.

Hope that helps a bit!

Jeremy

Agree!

And it is safer, and you have quad redundancy. Right now I have three 8S packs in the same configuration.
Bert06840 is offline   Reply With Quote
Old 09-02-2021, 03:55 AM   #20
Bus Nut
 
Rock-N-Ruth's Avatar
 
Join Date: Jul 2019
Location: Freedom Field, New Mexico
Posts: 459
Year: 1998
Coachwork: International
Chassis: Amtrans
Engine: 444E
Rated Cap: 84 pas
Quote:
Originally Posted by jjaj823 View Post
Greetings all!

I have 4 x 8s/24v batteries that I put together, with each set of 8 cells attached to a BMS. I accidentally tripped one of the battery breakers manually (i.e. it did not trip due to an electrical fault) when it was depleted.

Now, it appears that at least one of the batteries is unbalanced with the rest, which is causing my inverters to shut down as they sense low voltage. I spoke with the inverter rep and he recommended ordering 5 48v/4 cell balancers and running daisy chaining them together to balance all the cells.

But, in addition to being expensive, it seems like the BMS already balances each cell it is connected too, so shouldn't I just be able to balance the batteries as a unit? If so, does anyone have a link or recommendation on what to use for that? I can only seem to find balancers designed for 12v batteries.

Any other suggestions or recommendations are appreciated!

Jeremy
So if I understand you correctly, you accidentally removed one of your 8s batteries from the charging circuit and cased it to be drawn down but not recharged along with the other three? If this is the case the solution is simple. Top balance your batteries manually.
Remove all the batteries from the load circuit.
Remove the three from the charging circuit. Allow the low battery to charge to the place where it has the same voltage as the other three.
Then place all four batteries in parallel, not under load or charging, for 24 hours.
Measure the voltage on each battery. They should now be the same and you can configure them back into your system.
Rock-N-Ruth is offline   Reply With Quote
Reply

Tags
24v, balancer, inverter, lifepo4


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -5. The time now is 04:16 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.