First, be sure the batteries are actually fully charged. Checking the voltages at the inverter connections with a digital volt-meter, you should read 13.5-13.8 volts. If this checks properly, then use the DC amp function on the DVM to check the current draw of the inverter. When hooked in series with the inverter, the current should show no higher than 60-70 amps for the lowest normal draw of the inverter (800 watts). If both of these checks return normal results, you probably have a faulty inverter.
Best of Luck
Lee

__________________
"Adversity that does not kill you can only make you stronger."
Good Lord! I must be Superman by now!!!
Nachtwulf is offline   Reply With Quote
Old 08-23-2009, 11:22 PM   #2
Bus Geek
 
the_experience03's Avatar
 
Join Date: Feb 2006
Location: Saint James, MN
Posts: 2,669
Send a message via MSN to the_experience03 Send a message via Yahoo to the_experience03
Re: Electrical Drama--Help!

Quote:
Originally Posted by Nachtwulf
First, be sure the batteries are actually fully charged. Checking the voltages at the inverter connections with a digital volt-meter, you should read 13.5-13.8 volts. If this checks properly, then use the DC amp function on the DVM to check the current draw of the inverter. When hooked in series with the inverter, the current should show no higher than 60-70 amps for the lowest normal draw of the inverter (800 watts). If both of these checks return normal results, you probably have a faulty inverter.
Best of Luck
Lee
With the bus running and the alternator spinning. My inverters will do the same thing with a bad ground. Lower voltage due to bad connections means that higher current is required to get the same power and the inverters will shut down from overcurrenting. A similar test that will show just exactly where your loses are is to do a voltage drop test. Put one lead of the meter on the positive battery post. Put the other lead on the positive post of the inverter. This will create a second, high resistance path for electricity in parallel with the first. If the meter reads any more than about .25 volts I would say you have poor connections though it shouldn't cause the issue you're describing. 1 volt might though. Do the same test on the ground side with one lead on the negative battery post and the other on the negative terminal of the inverter and see what you get. I should mention that the inverter needs to be on and running, preferably with the biggest load you can put on it at the time you're doing these tests.
__________________
https://farm4.static.flickr.com/3024/...09f20d39_m.jpg
Skooling it...one state at a time...
the_experience03 is offline   Reply With Quote
Old 08-24-2009, 05:33 AM   #3
Ob1
Skoolie
 
Join Date: Aug 2009
Posts: 187
Year: 1963
Coachwork: Grumman
Chassis: Chevrolet
Engine: Chevy 292 I-6
Re: Electrical Drama--Help!

Other hints:
Keep the distance between your batteries and the inverter to a minimum, without being in the same compartment. Batteries emit explosive gasses, and corrosive gasses.

Shorter distance of the 12VDC cables means less line loss.

Cables should appear to be "overkill" sized. Large cables reduce line loss and can handle the loads without heating up. Best place I have found is a welder's supply shop, get arc welding ground cable. It can handle the load, is made with great insulation, and is very supple. Solder lugs on the ends for connections.

install a fuse on the + cable close to the battery. Car stereo shops carry nice high amperage fuses that are friendly for RV use {but generally not cheap}
Ob1 is offline   Reply With Quote
Old 08-25-2009, 09:10 PM   #4
Bus Crazy
 
Join Date: Jan 2008
Location: Adirondack Mountains NY
Posts: 1,101
Re: Electrical Drama--Help!

The surest easy way to measure the battery charge with wet cells is testing the cells with a hydrometer. There are electronic meters available that remain connected to the battery, and count amps in and amps out. After calibration they calculate percent of charge, but they are for upper budgets.

Otherwise, a full battery bank will measure about 12.7 volts after 24 hours with no charge and no load. Batteries will read a "surface" or "face" charge of 13+ volts right after coming off of a charger, even if the capacity has not been fully refilled.

Also, deep-cycle batteries are usually rated at C/20 - constant discharge at 1/20 of the rating for 20 hours. So a pair of 200 AH 6-volt batteries will give 10 amps at 12 volts for 20 hours. They will usually not last a full 60 minutes at a 200 amp draw.

It needs to be said over and over and over - clean and tighten all your connections. You would be surprised at the number of starters, alternators, and batteries that have been replaced unnecessarily because of a spot of corrosion on a connection.
__________________
Someone said "Making good decisions comes from experience, experience comes from bad decisions." I say there are three kinds of people: those who learn from their mistakes, those who learn from the mistakes of others, and those who never learn.
Redbear is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical Help levitayelor Electrical, Charging and Solar 34 02-09-2012 06:21 AM
Electrical frank-id Conversion General Discussions 6 04-27-2007 08:11 AM
360 Electrical Steve Everything Else | General Skoolie Discussions 0 03-07-2006 12:48 PM
Need Electrical Help !! pixie Conversion General Discussions 19 06-04-2005 11:27 AM
Electrical help, please? lapeer20m Everything Else | General Skoolie Discussions 0 04-29-2004 12:03 PM

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -5. The time now is 11:08 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.