I do have 200 amp fuses and breakers and I will not use 300 amps.
|
A 200A fuse cannot reliably protect a 4AWG wire either. The fuse has to be sized relative to the wire and the load.
The way to size a fuse is to size it (greater than) > 1.25x the max current of the circuit and < (less than) the rating of the wire. 4AWG is rated for between 100 and 160 depending on the wire you use.
A fuse is an intentional weak point, so in order to serve its purpose it has to be weaker than the rest of the system its meant to protect.
So you either need larger wire or smaller fuses. I suggest
this short video or this short article (
part 1: wire,
part 2: fuses/breakers)
Here is an Ampacity chart to see how much a wire can safely carry, it does not consider voltage drop which is not a safety factor but is a factor to be considered
Quote:
The neutrals and ground for the AC side are not displayed in the drawing.
|
I mostly ignored the AC side as I dont feel comfortable or qualified giving advice there. However the ground connection I am referring to is on the DC side of the inverter (consult the inverter documentation, or have the person who designed your system do so as this is certainly something they should've considered).