Old 08-14-2022, 06:26 PM   #1
Almost There
 
Join Date: Jun 2019
Location: AZ
Posts: 93
Year: ‘09
Coachwork: Bluebird
Chassis: Vision
Engine: 6.7
Rated Cap: 35’
Electrical Review

Would like any comments on my electrical diagram. I have left out the smaller draws on the AC and DC sides as I have those figured out. I will have a charge controller on the house batteries. I will have shore power available for my AC power only. so, questions:

1. Distance from the start batteries to the DC battery charger is 30'. That would be a total run of 60'. What size wire would you run? I was thinking 2/0.

2. Distance from DC fuse box to refrigerator is 35'. Total run of 70'. What size wire would you run? I was thinking 0. I don't know when I would use DC for the refrigerator, but I at least want it available.

3. The DC->DC charger looks like it will only take up to 6AWG wire. Any idea how to get bigger wires attached to it?

Thank you for your thoughts.
Attached Thumbnails
Buselectric.jpg  

Ranchorossa is offline   Reply With Quote
Old 08-14-2022, 07:45 PM   #2
Bus Crazy
 
Rwnielsen's Avatar
 
Join Date: Jun 2020
Location: Long Beach, CA
Posts: 1,075
Year: 1998
Coachwork: Blue Bird
Chassis: TC2000, 40' MPV
Engine: 5.9 Cummins/B300 trans
Rated Cap: U/K
Personally, I would separate the start battery entirely. Use it for its original purpose only. Make the living area completely separate...it's own battery bank, charger, etc..
If you feel you need to charge the bus battery, do it with a battery charger. I have a little 30w solar panel with a cheap controller to maintain my start battery.

I can't imagine a scenario where you'd need #0 wire for a DC refer
Rwnielsen is offline   Reply With Quote
Old 08-14-2022, 08:11 PM   #3
Almost There
 
Join Date: Jun 2019
Location: AZ
Posts: 93
Year: ‘09
Coachwork: Bluebird
Chassis: Vision
Engine: 6.7
Rated Cap: 35’
Refrigerator pulls 20amps dc. Just going by AWG wire charts for 35'. Any other ideas?
Ranchorossa is offline   Reply With Quote
Old 08-15-2022, 02:52 AM   #4
Bus Crazy
 
Rwnielsen's Avatar
 
Join Date: Jun 2020
Location: Long Beach, CA
Posts: 1,075
Year: 1998
Coachwork: Blue Bird
Chassis: TC2000, 40' MPV
Engine: 5.9 Cummins/B300 trans
Rated Cap: U/K
Quote:
Originally Posted by Ranchorossa View Post
Refrigerator pulls 20amps dc. Just going by AWG wire charts for 35'. Any other ideas?
First off, you could use your chassis as a DC ground and not double your run length. Secondly, you could go with a 24 volt system. Just ideas
Rwnielsen is offline   Reply With Quote
Old 08-15-2022, 09:12 AM   #5
Bus Crazy
 
TheHubbardBus's Avatar
 
Join Date: Apr 2019
Location: SW USA
Posts: 2,064
Year: 2003
Coachwork: IC / Amtran
Chassis: CE300
Engine: International T444e
Rated Cap: 23
Check out the ' Blue Sea Circuit Wizard' app (android or apple). Its an excellent tool so long as you do your part supplying the correct parameters.
__________________
Go away. 'Baitin.

Our Build: Mr. Beefy
TheHubbardBus is offline   Reply With Quote
Old 08-15-2022, 12:26 PM   #6
Almost There
 
Join Date: Jun 2019
Location: AZ
Posts: 93
Year: ‘09
Coachwork: Bluebird
Chassis: Vision
Engine: 6.7
Rated Cap: 35’
Have it set up for 12v. I'm great at ac wiring, so I'm gonna stick with bringing the ground back to the bus bar.

Blue Sea says I need wire capable of 180 amps.

Can welding wire be used for these long runs?
Ranchorossa is offline   Reply With Quote
Old 08-15-2022, 02:35 PM   #7
Bus Nut
 
Join Date: Sep 2015
Posts: 404
Year: 1992
Coachwork: Bluebird Mini-Bird 24'
Chassis: Chevy P30
Engine: Chevy 6.2L Diesel
Quote:
Originally Posted by Ranchorossa View Post
Have it set up for 12v. I'm great at ac wiring, so I'm gonna stick with bringing the ground back to the bus bar.

Blue Sea says I need wire capable of 180 amps.

Can welding wire be used for these long runs?
Copper is copper, generally speaking. Welding wire is normally stranded, which is what you want for any kind of mobile application.
Albatross is offline   Reply With Quote
Old 08-15-2022, 02:41 PM   #8
Bus Crazy
 
HamSkoolie's Avatar
 
Join Date: Jul 2021
Location: Southern Oregon
Posts: 1,607
Year: 1996
Coachwork: AmTran (Now Navistar)
Engine: DT444E (7.3L) International
Rated Cap: 31,800 pounds
Quote:
Originally Posted by Rwnielsen View Post
First off, you could use your chassis as a DC ground and not double your run length. Secondly, you could go with a 24 volt system. Just ideas

I believe for engineering purposes using the chassis as ground doesn't reduce the "circuit distance" (thus size of wire) ONLY the amount of wire needed to make the circuit thus reducing cost and freeing space in the passages used to route the wire.
I could be wrong but I'd need to see a reference
__________________
YouTube: HAMSkoolie WEB: HAMSkoolie.com
We've done so much, for so long, with so little, we now do the impossible, overnight, with nothing. US Marines -- 6531, 3521. . . .Ret ASE brakes & elect. Ret (auto and aviation mech). Extra Class HAM, NAUI/PADI OpenWater diver
HamSkoolie is offline   Reply With Quote
Old 08-15-2022, 03:05 PM   #9
Bus Crazy
 
Join Date: Apr 2020
Location: Northern California (Sacramento)
Posts: 1,424
Year: 1999
Coachwork: El Dorado Fiberglass
Chassis: Ford E450
Engine: V10 Gas
Quote:
Originally Posted by Ranchorossa View Post
Would like any comments on my electrical diagram. I have left out the smaller draws on the AC and DC sides as I have those figured out. I will have a charge controller on the house batteries. I will have shore power available for my AC power only. so, questions:

1. Distance from the start batteries to the DC battery charger is 30'. That would be a total run of 60'. What size wire would you run? I was thinking 2/0.

2. Distance from DC fuse box to refrigerator is 35'. Total run of 70'. What size wire would you run? I was thinking 0. I don't know when I would use DC for the refrigerator, but I at least want it available.

3. The DC->DC charger looks like it will only take up to 6AWG wire. Any idea how to get bigger wires attached to it?

Thank you for your thoughts.
Not sure if you've already committed to some of the purchases, but if you haven't yet bought the components, here's my questions/thoughts.

-Your battery is only 200Ah. A 60 amp DCDC charger would completely recharge it in less than three hours. Do you really need that large a DCDC charger? It's going to drive up your installation costs significantly.

Depending on how you recharge, you may be able to use a (much) smaller DCDC charger and get what you need. I have a 20 amp unit because I'm assuming I'll use the device to recharge when I move from site to site, and usually that will be several hours driving. In your case, if you truly need fast recharging while driving, you may need a large DCDC charger, but it will come at a cost.


-These wire distances are killer for the 12 volt fridge. Why not consider a standard 120 volt AC appliance? If you increase the size of the inverter you could install a (cheaper) 120 volt fridge and put it almost anywhere on the bus. Typically, the concern about 120 volt fridges is the vampire load on the inverter, but as long as you're running 200Ah or greater I can't see that as a valid argument, especially with solar.

Also, with 12v DC the voltage drop on the line combined with the lower voltage at the battery when it's getting low on charge may cause the fridge to operate under greater stress. There are a lot of things that feed into this, but you're kind of fighting the laws of physics at these distances.

The #6 lug limitation is telling you that whatever size wire is coming from the alternator or going to the battery, if it is greater than #6 you'll need an intermediary bus bar to handle the termination on the bigger cable, then connect the DCDC charger to that with something much shorter-in the case of a 60A charger, a #6 no more than about a meter long.

edit: don't forget to add a fuse at the alternator, then again at the beginning of the wire from the dcdc charger to the battery bus.
Rucker is offline   Reply With Quote
Old 08-15-2022, 03:17 PM   #10
Bus Crazy
 
Rwnielsen's Avatar
 
Join Date: Jun 2020
Location: Long Beach, CA
Posts: 1,075
Year: 1998
Coachwork: Blue Bird
Chassis: TC2000, 40' MPV
Engine: 5.9 Cummins/B300 trans
Rated Cap: U/K
Quote:
Originally Posted by HamSkoolie View Post
I believe for engineering purposes using the chassis as ground doesn't reduce the "circuit distance" (thus size of wire) ONLY the amount of wire needed to make the circuit thus reducing cost and freeing space in the passages used to route the wire.
I could be wrong but I'd need to see a reference
My thinking on this is that you derate the for voltage drop in one direction. You don't need to derate the chassis. You do not need 1/0 for a refer.
I've dabbled with electricity for a while, don't make simple things, complex.
Rwnielsen is offline   Reply With Quote
Old 08-15-2022, 03:36 PM   #11
Almost There
 
Join Date: Jun 2019
Location: AZ
Posts: 93
Year: ‘09
Coachwork: Bluebird
Chassis: Vision
Engine: 6.7
Rated Cap: 35’
The house battery is 300a. The refrigerator is a 3 way, already installed so 99% of the time it will run on ac or propane. Just came home from the rv repair shop. Recommended 4 or 6 for the refrigerator run and 2 for the run from batteries to the dc charger.

I have not bought the dc/dc charger yet. When we boondocks, wanted to run the engine as little as possible to charge the batteries, hence the big charger. I do have a small generator if needed. I'd rather have overkill and do it once, than to have to do it over again, or even worse, have a melt down.
Ranchorossa is offline   Reply With Quote
Old 08-15-2022, 03:50 PM   #12
Bus Crazy
 
Rwnielsen's Avatar
 
Join Date: Jun 2020
Location: Long Beach, CA
Posts: 1,075
Year: 1998
Coachwork: Blue Bird
Chassis: TC2000, 40' MPV
Engine: 5.9 Cummins/B300 trans
Rated Cap: U/K
Quote:
Originally Posted by Ranchorossa View Post
Refrigerator pulls 20amps dc. Just going by AWG wire charts for 35'. Any other ideas?
You mention that its a 3-way refer. Is the heater in it 240 watt? Or...is that the recommended circuit ampacity? Real time numbers make a difference in these calculations.
Rwnielsen is offline   Reply With Quote
Old 08-15-2022, 03:52 PM   #13
Bus Crazy
 
HamSkoolie's Avatar
 
Join Date: Jul 2021
Location: Southern Oregon
Posts: 1,607
Year: 1996
Coachwork: AmTran (Now Navistar)
Engine: DT444E (7.3L) International
Rated Cap: 31,800 pounds
Voltage drop at those long distances is definitely a concern. It's one reason our plan includes a 24 volt "main line" feeding several 12 volt fuse panels via 24 to 12 volt converters. The idea being that voltage drop is minimized by the larger main line running higher voltage and then smaller gauge wires from each of the 12 volt panels to the individual points of use.
The main line will be run from the batteries up and then forward and back to the different panels and be of large enough gauge to handle the necessary loads. From there smaller wires can carry the small individual loads and be a lot easier to run between the insulation and interior panels.

Part of the reasoning is that, being a pack rat when it comes to such things as wire, I already have a good amount of pure copper heavy gauge stranded wire but I'd have bought wire if it seemed the better option. We will be buying new metal clad cable for everything in the 120 circuitry even though I have hundreds of feet of 12 gauge solid core romex on hand because the metal clad is stranded wire and offers superior protection against penetration without having to install nail guards and/or conduit.


Just the way we're designing our system.... YMMV
__________________
YouTube: HAMSkoolie WEB: HAMSkoolie.com
We've done so much, for so long, with so little, we now do the impossible, overnight, with nothing. US Marines -- 6531, 3521. . . .Ret ASE brakes & elect. Ret (auto and aviation mech). Extra Class HAM, NAUI/PADI OpenWater diver
HamSkoolie is offline   Reply With Quote
Old 08-15-2022, 04:05 PM   #14
Almost There
 
Join Date: Jun 2019
Location: AZ
Posts: 93
Year: ‘09
Coachwork: Bluebird
Chassis: Vision
Engine: 6.7
Rated Cap: 35’
Good ideas. I'm already set up for 12v. I too have a junk ton of 12 and 14 Romex for the 120. Also have a couple hundred feet of conduit sitting around. So, Romex in conduit = super safe. Overkill I know.
Ranchorossa is offline   Reply With Quote
Old 08-15-2022, 04:08 PM   #15
Bus Crazy
 
HamSkoolie's Avatar
 
Join Date: Jul 2021
Location: Southern Oregon
Posts: 1,607
Year: 1996
Coachwork: AmTran (Now Navistar)
Engine: DT444E (7.3L) International
Rated Cap: 31,800 pounds
Quote:
Originally Posted by Ranchorossa View Post
Good ideas. I'm already set up for 12v. I too have a junk ton of 12 and 14 Romex for the 120. Also have a couple hundred feet of conduit sitting around. So, Romex in conduit = super safe. Overkill I know.

I don't think romex is supposed to be in conduit. Conduit is for individual wires.
Not an electrician, just a guy that's done a lot of home repairs to wiring, not all of which was installed by an electrician (exposed splices laying around in the attic, extension cords used to run circuits, etc.
For the 120 side of things, see if you can find a "green book". They're pretty handy.
__________________
YouTube: HAMSkoolie WEB: HAMSkoolie.com
We've done so much, for so long, with so little, we now do the impossible, overnight, with nothing. US Marines -- 6531, 3521. . . .Ret ASE brakes & elect. Ret (auto and aviation mech). Extra Class HAM, NAUI/PADI OpenWater diver
HamSkoolie is offline   Reply With Quote
Old 08-15-2022, 04:26 PM   #16
Bus Crazy
 
Rwnielsen's Avatar
 
Join Date: Jun 2020
Location: Long Beach, CA
Posts: 1,075
Year: 1998
Coachwork: Blue Bird
Chassis: TC2000, 40' MPV
Engine: 5.9 Cummins/B300 trans
Rated Cap: U/K
Quote:
Originally Posted by Ranchorossa View Post
Good ideas. I'm already set up for 12v. I too have a junk ton of 12 and 14 Romex for the 120. Also have a couple hundred feet of conduit sitting around. So, Romex in conduit = super safe. Overkill I know.
Romex in conduit is highly controversial. There are rules that prevent it and others saying it's OK as protection (in certain cases). Either way, it will be a nightmare to pull in. I'm using stranded #12 MC, 12/2 & 12/3 cable, it doesn't easily kink and it's what I use at work. I know the owner, so it's cheap . If you're going to run conduit just pull in individual wire. Be mindful of derating..."more than 3 current carrying conductors..."
Rwnielsen is offline   Reply With Quote
Old 08-15-2022, 05:29 PM   #17
Almost There
 
Join Date: Jun 2019
Location: AZ
Posts: 93
Year: ‘09
Coachwork: Bluebird
Chassis: Vision
Engine: 6.7
Rated Cap: 35’
At least in our county, don't know about in skoolies, Romex can go into conduit. For long runs, I thread wire through individual sections of conduit. When all the wire is where it needs to be, I glue the sections together. Super easy, no fish tape needed.
Ranchorossa is offline   Reply With Quote
Old 08-15-2022, 06:10 PM   #18
Bus Crazy
 
Rwnielsen's Avatar
 
Join Date: Jun 2020
Location: Long Beach, CA
Posts: 1,075
Year: 1998
Coachwork: Blue Bird
Chassis: TC2000, 40' MPV
Engine: 5.9 Cummins/B300 trans
Rated Cap: U/K
Quote:
While the National Electrical Code does not expressly forbid inserting NM cable inside conduit, it is, in practice, very difficult to do so and very few professional electricians will do such an installation.
Like you said, it's up to you. If you have a method that works, and you have free materials, go for it.
Rwnielsen is offline   Reply With Quote
Old 08-15-2022, 07:18 PM   #19
Bus Crazy
 
DeMac's Avatar
 
Join Date: Oct 2020
Location: Florida
Posts: 1,558
Coachwork: Integrated Coach Corp.
Chassis: RE-300 42ft
Engine: 466ci
Rated Cap: 90
Great Choice for Wire Protection

Quote:
Originally Posted by Rwnielsen View Post
Romex in conduit is highly controversial. There are rules that prevent it and others saying it's OK as protection (in certain cases). Either way, it will be a nightmare to pull in. I'm using stranded #12 MC, 12/2 & 12/3 cable, it doesn't easily kink and it's what I use at work. I know the owner, so it's cheap . If you're going to run conduit just pull in individual wire. Be mindful of derating..."more than 3 current carrying conductors..."
Agreed:
Conduit fill adds up fast, too. Bump to 3/4"+ for those runs with two or more cables, plus derating, if applicable. Where they pass through boxes, twice as many neutrals. Plus double the grounds to bond, at each junction. Unless each cable is in their own raceway. Then landing all the conduit in the panel might be exciting. Just connecting the pipe to j-boxes, in a bus, is fun.

The conduit protects the conductors from damage, per its classification. (NEC 300.4 Protection Against Physical Damage)
Idk what additional protections the Romex offers over THHN, once inside of the conduit. Aside from conversely holding in the heat.

I put cable into conduit, too. Sometimes, there's no way around it. Romex free-air (stapled) in an attic, then pipe down a wall's surface to a j-box. UF wire, too. Kitchen appliance gfci down through pvc in dirt/concrete to island recepts. Just not my ideal plan for an entire facility. Vacuuming a string, then pulling thhn is quick, easy & economical.


On our rig, where I switch from mc to emt, I use a 3/8" flex to 1/2" emt changeover. Strip out the req'd length, add an anti-short & push.
__________________
Ceiling: Framing & Electrical Rough-in
Convert Hatch to AC & Roof Patch
🇺🇸 Frederick Douglass: "If there is no struggle, there is no progress.”
DeMac is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -5. The time now is 06:47 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.