Originally Posted by docmurphy
.....Please let me know what you guys think...
Thanks
|
I deleted my first reply because I don't want to sound discouraging. If you provide more info we may be able to better help. The inverter documentation as written, a picture of the line (supply), the more the better.
In the pic there are the issues already mentioned.
No ground bar, unterminated neutral & ground, bonding done at main breaker, etc.
The 'sub panel' itself, is it a disconnect? 30a or 50a?
Looks like a surface mount box, am I correct?
Is the box currently being wired, but not yet mounted?
-Maybe just a dry/test fit.
The bottom fed, line side 'feeder' is 10/3 romex,
will it stay exposed/unprotected?
The four (4), top fed, load side circuits:
Are they all 4 pushed thru the same 1" connector?
What kind of connector is used?
Those four romex look all the same,,
are they all 14/2 or 12/2? ok if 12.
You have twin 15a and 20a brkrs installed on, ?
What is the rated amp of the jaw/bus under each breaker?
How are you physically protecting the load wires?
Is the line side, suplly: split phase or same phase run parallel using single neutral?
Line side is protected with one 30a 2 pole breaker?
Help us help you. Any additional info on what you're intending to use this as, I'm sure we can help as a group..