Thanks for all the replies.
1) I looked up inverter compressor refrigerators. The ones I saw were all full sized and expensive. Do you have a lead on something around the 4.5 cuft size with an inverter compressor?
2) The electrical math and lingo, at least for me, is tied with my understanding of women. Lots of short circuits on both counts.
3) I've heard of three ways to come up with start-up / surge wattage.
a) Rated Load Amperage (RLA) x 1.5. This seems reasonable. My home fridge is 4.5a x 1.5 = 6.75a x 115v = 776.25w start-up/surge
b) LRA - Locked Rotor Amperage (found on the compressor lable) x voltage. A small fridge with a 350btu compressor will have an LRA of ~8a. So, around 900w start-up/surge.
LRA - Locked Rotor Amps: The max current you can expect if the rotor is locked up.
c) 8 - 10 times the rated wattage. Xantrex support used 10 in their example. Online I find a mini-fridges run between 85-100w, an average house fridge is ~150w running with 800-1200 start-up / surge. Yet, at 8 - 10 times it would be more like 1200 - 1500w.
So, between the three ways, we've got 776.25w, 900w and 800-1500w.
My friend is a refrigeration contractor. He says what you want to know is the LRA. Multiply that by the voltage and that tells you the maximum your compressor will pull if the rotor is stuck (i.e., lockup). Your actual start-up surge will likely be a bit lower.
If you calculate your inverter wattage based on LRA amperage, you should be fine with your start-up wattage.
Rucker said his mini-fridge was pulling 8a at start-up and dropped to 1.5a when running. This would be ~3.5x.
Cadillac said 3.5 - 4x cold, 10x hot environment temp.
Ironically, I was searching a bit more as I was writing this and this question/answer came up on E-Trailers website:
https://www.etrailer.com/question-442653.html
Question:
Can someone look at the nameplate on the Everchill 4.5 cubic ft 120V fridge, part # 324-000109, model BC-128B and tell me the LRA locked rotor amps? Am looking to size an inverter for this. I think the average current draw is 0.8 amps 96 watts and 24 hr running average is ballpark 0.69 Kwhrs about 30 watts so avg running power is 30 to 96 watts but locked rotor amps help determine the inverter size required. Thanks.
Expert Reply:
The Everchill RV Mini Refrigerator part # 324-000109 will pull around 8-9 amps on startup (LRA) and then around 1 amp while running.
LOL! I wish I had found this a few days ago. Lots of thinking and calculating could have been saved.
SUMMARY:
I think all three get you in a start-up surge ballpark.
I think the 1.5x method is maybe a bit on the low side. The LRA seems to be right about there for average environmental temperatures and the 8-10x is more worst case high environmental temp situations.
I guess if you're choosing an inverter, the worst case scenario is the one on which to base that decision.
Hope this helps someone else. I'm done!