A few more pictures ..

Propane line (copper)

I ran PEX A water lines to a valve then used stainless braided supply lines to go to the water heater, faucets, etc.
Attached Thumbnails
20200613_112858.jpg   20200613_112834.jpg   20200613_112802.jpg  

Frochevy is offline   Reply With Quote
Old 04-09-2022, 06:06 PM   #22
New Member
 
Luddite's Avatar
 
Join Date: Apr 2022
Posts: 1
Those copper LP lines will work harden then break. Look into replacing with hoses designed for LP.
Luddite is offline   Reply With Quote
Old 04-10-2022, 07:55 AM   #23
Bus Nut
 
Frochevy's Avatar
 
Join Date: May 2018
Location: Wamego Ks
Posts: 617
Year: 2007
Chassis: Collins
Engine: 6.6L LMM Duramax
Quote:
Originally Posted by Luddite View Post
Those copper LP lines will work harden then break. Look into replacing with hoses designed for LP.
Are you saying they will work harden from the slight flexing that may occur when the bus chassis flexes?

I don't want to turn this into a negative discussion, but I do have to ask this question(s): don't you have to bend a metal past it's ductility to plastically deform it? And don't you have to physically bend a piece of metal back and forth multiple times (plastic deformation) to eventually break it? If I flex a piece of 1" steel strap without going past that point where it bends and stays, will it ever break?

I'm basing my questions off of steel. Because I work with steel in the manufacturing industry. I don't know copper characteristics, but assume it is a metal just like steel and that's why I'm asking the question. I've heard the same comment about using Romex in a bus/camper etc. I'm really wanting to find the real answer on this and Romex, but I don't want to start a negative argument about it as I really don't know and the thought of cracking propane lines scares me!! So either way, thank you for taking the time to ask.
Frochevy is offline   Reply With Quote
Old 04-10-2022, 10:50 PM   #24
Bus Crazy
 
Join Date: Feb 2018
Location: Golden Valley AZ
Posts: 1,036
Year: 1993
Chassis: ThomasBuilt 30'
Engine: need someone to tell me
Rated Cap: me + 1
Quote:
Originally Posted by Frochevy View Post
Are you saying they will work harden from the slight flexing that may occur when the bus chassis flexes?

I don't want to turn this into a negative discussion, but I do have to ask this question(s): don't you have to bend a metal past it's ductility to plastically deform it? And don't you have to physically bend a piece of metal back and forth multiple times (plastic deformation) to eventually break it? If I flex a piece of 1" steel strap without going past that point where it bends and stays, will it ever break?

I'm basing my questions off of steel. Because I work with steel in the manufacturing industry. I don't know copper characteristics, but assume it is a metal just like steel and that's why I'm asking the question. I've heard the same comment about using Romex in a bus/camper etc. I'm really wanting to find the real answer on this and Romex, but I don't want to start a negative argument about it as I really don't know and the thought of cracking propane lines scares me!! So either way, thank you for taking the time to ask.
"don't you have to bend a metal past it's ductility to plastically deform it?"
this is true to deform it...but he is talking about breaking or cracking it, not deforming it.

A good completely hardened piece of high carbon steel will break before it will take a permanent bend.


If I remember correctly from my strength of materials class in the early 70's, ductility refers to a metals ability to be mashed into thin sheets/foil with out hardening/tearing. Plasticity is the materials ability to deform to and maintain a different shape (think lump 0f soft modeling clay) as opposed to elasticity which is the ability to stretch and still return to its original shape. Think rubber band.

Cold forming/rolling hardens many different types of metals by work hardening, as opposed to hot forming/rolling.


I think he is referring to a form of cold work hardening referred to as "fatigue hardening" (which is also what happens in your bending example, only it is much faster and usually intentional) a condition, that is usually caused by vibration, where the metal forms small cracks and then fails. They used to refer to a helicopter as a "fatigue machine" because parts constantly have to be replaced before they break from fatigue hardening.) The 2 most often used vibration solutions used in air compressor tubes connecting the vibrating compressor and the stationary non vibrating tank and the like are 1) use a substitute flexible material usually rubber or plastic or 2) coil the metal in a few loops/coils to absorb the vibration - old school.

That said, when I read his comment, I really couldn't see that much vibration, however, a failure here could be catastrophic, so it might be better to use a rubber hose (which is pretty common). After all, propane has as least 3 ways to ruin your day - fire, explosion, and asphyxiation. TOXIC??


I am using the word catastrophic in the sense that it is sudden, (little or no warning) with complete and disastrous results.
kidharris is offline   Reply With Quote
Old 04-10-2022, 10:54 PM   #25
Bus Nut
 
Frochevy's Avatar
 
Join Date: May 2018
Location: Wamego Ks
Posts: 617
Year: 2007
Chassis: Collins
Engine: 6.6L LMM Duramax
Quote:
Originally Posted by kidharris View Post
"don't you have to bend a metal past it's ductility to plastically deform it?"
this is true to deform it...but he is talking about breaking or cracking it.


I think he is referring to a form of work gardening referred to as "fatigue hardening" (which is also what happens in your bending example, only it is much faster) a condition that is usually caused by vibration (they used to refer to a helicopter as a "fatigue machine" and parts constantly have to be replaced before they break) and form small cracks and then fail. The 2 most often used solutions in air compressors and the like are 1) use a substitute material usually rubber or plastic or 2) coil the metal in a few coils to absorb the vibration - old school.


That said, when I read his comment, I really couldn't see that much vibration, however, a failure here could be catastrophic, so it might be better to use a rubber hose (which is pretty common).


I am using the word catastrophic in the sense that is sudden, (little or no warning) with complete and disastrous results.
I appreciate the response and that makes sense. What kind of rubber hose and fittings are people using? This would be fairly easy for me to change. I don't think there is much flexing or vibration, but it's not worth the risk of something were to happen like you guys mention.
Frochevy is offline   Reply With Quote
Old 04-11-2022, 01:24 AM   #26
Bus Crazy
 
Join Date: Feb 2018
Location: Golden Valley AZ
Posts: 1,036
Year: 1993
Chassis: ThomasBuilt 30'
Engine: need someone to tell me
Rated Cap: me + 1
Quote:
Originally Posted by Frochevy View Post
I appreciate the response and that makes sense. What kind of rubber hose and fittings are people using? This would be fairly easy for me to change. I don't think there is much flexing or vibration, but it's not worth the risk of something were to happen like you guys mention.



You might check with a local propane dealer or 2 to see what your options are.
kidharris is offline   Reply With Quote
Old 04-11-2022, 07:01 PM   #27
Skoolie
 
Join Date: Nov 2016
Location: ocala FL.
Posts: 147
Year: 2000
Coachwork: Thomas
Chassis: international
Engine: t444e
Rated Cap: short
I was given a stove and other items out of an old camper. The propane line going to the stove appeared to be copper and it looked to be a factory install. I was always told not to use copper in a mobile environment so this surprised me.
syntaxterror is offline   Reply With Quote
Old 04-12-2022, 01:51 PM   #28
Bus Crazy
 
Join Date: Apr 2020
Location: Northern California (Sacramento)
Posts: 1,424
Year: 1999
Coachwork: El Dorado Fiberglass
Chassis: Ford E450
Engine: V10 Gas
Quote:
Originally Posted by Frochevy View Post
Are you saying they will work harden from the slight flexing that may occur when the bus chassis flexes?

I don't want to turn this into a negative discussion, but I do have to ask this question(s): don't you have to bend a metal past it's ductility to plastically deform it? And don't you have to physically bend a piece of metal back and forth multiple times (plastic deformation) to eventually break it? If I flex a piece of 1" steel strap without going past that point where it bends and stays, will it ever break?

I'm basing my questions off of steel. Because I work with steel in the manufacturing industry. I don't know copper characteristics, but assume it is a metal just like steel and that's why I'm asking the question. I've heard the same comment about using Romex in a bus/camper etc. I'm really wanting to find the real answer on this and Romex, but I don't want to start a negative argument about it as I really don't know and the thought of cracking propane lines scares me!! So either way, thank you for taking the time to ask.
I'm not convinced copper supply lines like the one in the picture are particularly prone to work hardening and catastrophic failure.

Yes, we understand the science of it well enough to know there is a risk.

If the lines are properly supported and the amount of flex or movement between connections is low (read: secure your propane tanks from movement; use flexible rubber grommets to secure your lines) the likelihood of cracks or failure drops to almost nothing.

For the record my propane lines are all standard LP flex hoses, and I've installed them to be replaced every other year or so.
Rucker is offline   Reply With Quote
Old 04-13-2022, 10:51 AM   #29
Mini-Skoolie
 
Join Date: Jul 2021
Location: Kansas City
Posts: 51
Year: 1999
Chassis: International Genesis
Engine: Navistar D466
I have mine installed in a "closet" in the bathroom. I also have the Excel, which supposedly doesn't require venting. I did PEX for all of my water lines, with brass fittings and crimp/-style clamps. I find this is really resistant to freezing and easy to work with- plus the vibrations shouldn't be an issue. Fingers crossed!
Attached Thumbnails
water closet.jpg   bathroom.jpg  
Delos356 is offline   Reply With Quote
Old 08-14-2022, 06:35 PM   #30
Mini-Skoolie
 
Join Date: Feb 2020
Posts: 22
I have an excel water heater in my Skoolie and had an issue today while camping taking an outdoor shower. My gas inlet line melted, caught fire which then melted my hot water out pex line causing a mess. Anyone have any ideas why this would have happen. I’ve only used it for two showers so far and kitchen sink.
57ratrod is offline   Reply With Quote
Old 08-15-2022, 11:50 AM   #31
Mini-Skoolie
 
Join Date: Jul 2021
Location: Kansas City
Posts: 51
Year: 1999
Chassis: International Genesis
Engine: Navistar D466
Quote:
Originally Posted by 57ratrod View Post
I have an excel water heater in my Skoolie and had an issue today while camping taking an outdoor shower. My gas inlet line melted, caught fire which then melted my hot water out pex line causing a mess. Anyone have any ideas why this would have happen. I’ve only used it for two showers so far and kitchen sink.
WHOA! That sounds scary!

Can you post a pic of how it was hooked up? Propane gas shouldn't ever get hot, so I'm not sure how it would have melted unless it caught on fire first.
Delos356 is offline   Reply With Quote
Old 08-15-2022, 02:13 PM   #32
Bus Geek
 
Join Date: May 2009
Location: Columbus Ohio
Posts: 18,758
Year: 1991
Coachwork: Carpenter
Chassis: International 3800
Engine: DTA360 / MT643
Rated Cap: 7 Row Handicap
sounds like it experience Rollout which is where the flame burns backwards due to a positive pressure on the vent (or blocked vent).. or a clogged burner orifice.. it could also be that there was a leak that is past the gas valve and the gas lit-off there..



why was the gas inlet Plastic?? shouldnt it have been copper?
cadillackid is offline   Reply With Quote
Old 08-15-2022, 02:48 PM   #33
Bus Crazy
 
HamSkoolie's Avatar
 
Join Date: Jul 2021
Location: Southern Oregon
Posts: 1,607
Year: 1996
Coachwork: AmTran (Now Navistar)
Engine: DT444E (7.3L) International
Rated Cap: 31,800 pounds
Quote:
Originally Posted by cadillackid View Post
why was the gas inlet Plastic?? shouldnt it have been copper?

I would think copper or a flexible appliance (my choice) gas line (with valve at base of the flex line).
__________________
YouTube: HAMSkoolie WEB: HAMSkoolie.com
We've done so much, for so long, with so little, we now do the impossible, overnight, with nothing. US Marines -- 6531, 3521. . . .Ret ASE brakes & elect. Ret (auto and aviation mech). Extra Class HAM, NAUI/PADI OpenWater diver
HamSkoolie is offline   Reply With Quote
Old 08-15-2022, 04:04 PM   #34
Mini-Skoolie
 
Join Date: Feb 2020
Posts: 22
How do I post pictures, using an iPad
57ratrod is offline   Reply With Quote
Old 08-15-2022, 04:13 PM   #35
Mini-Skoolie
 
Join Date: Feb 2020
Posts: 22
Pics

Click image for larger version

Name:	77947CD0-ADAE-4D12-8129-EFB0104BDF2C.jpg
Views:	22
Size:	159.7 KB
ID:	67364

Click image for larger version

Name:	DC2AC809-6060-4F8A-A964-D0B3A1AEA944.jpg
Views:	16
Size:	116.2 KB
ID:	67365

Click image for larger version

Name:	AC2FE229-904D-48E2-A3AD-11506EE9D655.jpg
Views:	19
Size:	121.2 KB
ID:	67366
57ratrod is offline   Reply With Quote
Old 08-15-2022, 06:13 PM   #36
Mini-Skoolie
 
Join Date: Feb 2020
Posts: 22
More pics

Click image for larger version

Name:	447E760C-1FCA-4120-95E1-7520919345EA.jpg
Views:	14
Size:	258.6 KB
ID:	67376

Click image for larger version

Name:	84B43142-C975-4B90-8FE8-D66CBDE09C2B.jpg
Views:	10
Size:	271.3 KB
ID:	67377

Click image for larger version

Name:	3850821E-54BB-487C-B0C3-F0CB7C0B1C99.jpg
Views:	17
Size:	295.5 KB
ID:	67378

Click image for larger version

Name:	C774F292-6F5D-4D4A-9790-C7AF97A2506B.jpg
Views:	20
Size:	216.4 KB
ID:	67379
57ratrod is offline   Reply With Quote
Old 08-16-2022, 10:30 AM   #37
Bus Nut
 
Join Date: Oct 2018
Location: Central Alabama
Posts: 541
Year: 1998
Coachwork: Blue Bird
Chassis: TC/2000
Engine: 5.9 Cummins 12-valve
Rated Cap: 1
Quote:
Originally Posted by 57ratrod View Post
I have an excel water heater in my Skoolie and had an issue today while camping taking an outdoor shower. My gas inlet line melted, caught fire which then melted my hot water out pex line causing a mess. Anyone have any ideas why this would have happen. I’ve only used it for two showers so far and kitchen sink.
Electrical fire first then it melted the line?
BamaBus is offline   Reply With Quote
Old 08-16-2022, 12:35 PM   #38
Bus Geek
 
ol trunt's Avatar
 
Join Date: Apr 2012
Location: So Cal
Posts: 3,227
Year: 1935
Coachwork: Superior
Chassis: Chevy
Engine: 317 ci/tid / Isuzu
That would be my guess also--might see what the mfg has to say about it.
Jack
ol trunt is offline   Reply With Quote
Old 08-16-2022, 03:10 PM   #39
Skoolie
 
Join Date: Aug 2021
Location: Santa Fe
Posts: 134
Year: 2007
Coachwork: Thomas
Chassis: 31 ft. HDX
Engine: CAT C7 250 hp
Rated Cap: 36,300 GVW
It looks to me like the gas inlet fitting was never properly sealed. The brass fitting shown in the picture has a very distorted rubber seal in it, but there is no thread sealant on the fitting. Heat and flame go upwards, so the melted electrical parts are just collateral damage.
I would never use a rubber gas hose inside a vehicle.
Is that propane tank secured in any way?
jimmythomas is offline   Reply With Quote
Old 08-16-2022, 04:22 PM   #40
Bus Crazy
 
Join Date: Apr 2020
Location: Northern California (Sacramento)
Posts: 1,424
Year: 1999
Coachwork: El Dorado Fiberglass
Chassis: Ford E450
Engine: V10 Gas
Quote:
Originally Posted by jimmythomas View Post
It looks to me like the gas inlet fitting was never properly sealed. The brass fitting shown in the picture has a very distorted rubber seal in it, but there is no thread sealant on the fitting. Heat and flame go upwards, so the melted electrical parts are just collateral damage.
I would never use a rubber gas hose inside a vehicle.
Is that propane tank secured in any way?
I hate propane fittings for this reason.

Is the gas inlet on the heater 1/2" NPT? If so, that fitting is not the right type.
Rucker is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -5. The time now is 08:34 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.