Quote:
Originally Posted by Wnchstr156
Being an HVACR tech for commercial buildings I can tell you that any AC needs to be charged correctly to dehumidify. Also 99% of people do not charge these to the correct super heat and sub cooling. The manufacturer usually lists what it should be on the unit. I can't tell you the amount of times I have seen refrigerant charge that seems fine until the super heat is calculated. Once it is adjusted customers tell me it works better than it ever has.
|
Minisplits are a bit tricky because they vary both the compressor output and employ an EEV. Typically you can’t monitor head pressure . It’s rare to find a service manual that lists the superheat for them. They are a bit forgiving on overcharge due to having an accumulator but nevertheless I usually end up evac and weigh in a recommended charge. I’ve played with mine going over and under on charge and measuring performance. Thus far it seems like factory charge amount gives me best results.
The service books do usually tell you how much refrigerant to add for long line sets
An undercharged mini will cool decent but have very high sun cool in heat mode. A severely overcharged mini will trigger the computer to ramp down or periodically shut off the compressor ( it will be pulling high current).. takes quite a bit over to reach this point.
Superheat can be tested and charged for easier on the bus road AC. Superheat is usually set lower than on a commercial unit. These evaporators flow quite a bit of liquid at capacity more than you would ever flow in a fixed-system scenerio. Those are small compact coils with multi pass and very high volume blowers. Coil temperatures are often just above freezing.
This allows for the fluctuating capacity of the compressor to still maintain decent capacity for short idle periods..