Old 12-08-2022, 10:20 PM   #1
Skoolie
 
Join Date: Jul 2019
Location: Houston
Posts: 105
Year: 1997
Engine: Cummins 8.3
For heated floors with pex pipe, is it terrible to have a fitting spliced in a zone?

Hi all,

When running the pex for a long zone in my hydronic heated floors, I came up about 10 feet short of its destination. Having never installed hydronic floors, I’m curious if others would think there is a high enough potential for leaks at the fitting for me to spend the money to buy a new run of pex. The floor will be pretty sealed up once it’s in place.

Any help is appreciated,
Thanks again,

Slowpoke

Truffles is offline   Reply With Quote
Old 12-09-2022, 08:33 AM   #2
Bus Nut
 
TJones's Avatar
 
Join Date: Jul 2017
Location: Rapid City, SD
Posts: 993
Year: 2001
Coachwork: Blue Bird
Chassis: CS RE
Engine: ISC 8.3 L 260 hp
Rated Cap: 36
Quote:
Originally Posted by Truffles View Post
Hi all,

When running the pex for a long zone in my hydronic heated floors, I came up about 10 feet short of its destination. Having never installed hydronic floors, I’m curious if others would think there is a high enough potential for leaks at the fitting for me to spend the money to buy a new run of pex. The floor will be pretty sealed up once it’s in place.


Any help is appreciated,
Thanks again,

Slowpoke

Best practice is to not have fittings in inaccessible places. The cost of new pex is far less than having to locate and repair a leak down the road.

Ted
TJones is offline   Reply With Quote
Old 12-09-2022, 01:59 PM   #3
Bus Nut
 
fo4imtippin's Avatar
 
Join Date: Oct 2021
Location: Jacksonville, FL
Posts: 719
Year: 2003
Coachwork: BlueBird
Chassis: TC2000 28ft
Engine: Cummins ISB 5.9 24v, MD3060
Rated Cap: 14
PexA or Pex B? I would have no qualms about an PexA (expansion, Uponor, Propex etc) joint under a floor. I generally follow the no hidden splices thing and dont hide splices with PexB (crimp or cinch fittings).
fo4imtippin is offline   Reply With Quote
Old 12-25-2022, 09:56 PM   #4
New Member
 
Join Date: Nov 2015
Location: Georgia
Posts: 5
Year: 2004
Coachwork: International
Chassis: 300
Engine: DT466E
Rated Cap: 90 Pax
No splice

I’m a pipefitter with many years of installing and repairing hydronic heating and cooling systems. The industry rule of thumb is NEVER bury a splice of any kind unless the material is soldered, welded, brazed, or fused and the entire system has been pressure tested at max rating for a minimum of two hours. All pipe regardless of type has a safety margin of 125% above rated service pressure so don’t be afraid to test your system at the max pressure of the lowest rated part/fitting/joint. Hydronic heating systems expand and contract during each cycle as the system calls for heat and then shuts the loop down once the thermostat is satisfied. This constant movement will eventually cause fittings to leak, which isn’t a big deal if the leak is accessible and easily repaired.
ron70 is offline   Reply With Quote
Old 03-19-2023, 08:56 PM   #5
Skoolie
 
Join Date: Jul 2019
Location: Houston
Posts: 105
Year: 1997
Engine: Cummins 8.3
Quote:
Originally Posted by ron70 View Post
I’m a pipefitter with many years of installing and repairing hydronic heating and cooling systems. The industry rule of thumb is NEVER bury a splice of any kind unless the material is soldered, welded, brazed, or fused and the entire system has been pressure tested at max rating for a minimum of two hours. All pipe regardless of type has a safety margin of 125% above rated service pressure so don’t be afraid to test your system at the max pressure of the lowest rated part/fitting/joint. Hydronic heating systems expand and contract during each cycle as the system calls for heat and then shuts the loop down once the thermostat is satisfied. This constant movement will eventually cause fittings to leak, which isn’t a big deal if the leak is accessible and easily repaired.
Thanks for sharing your knowledge. I got a whole new roll to replace the short run with. I appreciate you.
Truffles is offline   Reply With Quote
Old 03-19-2023, 09:17 PM   #6
Bus Geek
 
Join Date: May 2009
Location: Columbus Ohio
Posts: 18,827
Year: 1991
Coachwork: Carpenter
Chassis: International 3800
Engine: DTA360 / MT643
Rated Cap: 7 Row Handicap
ha! we used to run into splices in HVAC linesets inside of walls.. talk about an installer that caused us (the later service company) lots of headache in troubleshooting a freon leak.....
cadillackid is offline   Reply With Quote
Reply

Tags
fitting, heated, hydronic, leak, pex

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -5. The time now is 04:00 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.