High SEER comes from pairing larger indoor coil(s) with smaller compressor(s). But it requires an expansion valve to operate properly.
all of the mini-splits with inverter compressors have electronic expansion valves in them.. the better ones use 3 sensors on each coil so you can figure out the true saturation point in the coil..
its a known fact that minisplits run most effiecient at between 30-80% rated capacity..
from what ive seen in taking units apart that many of the 9000 BTU units are exactly the same as the 12,000 BTU units.. a couple appear to have slightly smaller indoor units but 2 that I messed with were identical...
so run a computer program that limits the max capacity to 9000 BTU and the unit is running always at less than its true rated capacity and can register ultra-high SEER ratings..
the variable speed nature of minisplits means that really you can install 12,000 BTU units and even if the yare oversize they will just slow down the compressor and the fans to match the cooling load and still control humidity..
the ducted units in my house have very long run times but are constant and the watt usage is low.. even though if I ran all the units on full blast it is way oversized for the house (but gives me the quick cooldown I like because i dont run A/C in my house until its time to sleep).. even on somewhat cooler ultra humid days when I run them I never get a clammy house because my blowers and those compressors slow down to match the load..
the outdoor fans slow down to maintain enough head pressure and heat in the refrigerant so that you dont freeze across the EEV ..