That's a light load.. There's truly no good reason to use old style screw-in fuses. You can get away with a small 20-amp breaker box. Here's the one I have installed:
You can use two breakers instead of the 2-pole 20 amp breaker I used, but I'd advise against it. Mine is set up in the same way you will find many boats. Both neutral and hot are fed through a coupled breaker. This is for protection against reversed polarity outlets.
Let's take the example where I only have one breaker connected to the hot line. If I were to then plug the bus into an outlet with reverse polarity and overload the breaker it would trip the NEUTRAL line instead of the hot line, still feeding a live line to the outlets. Bad. A 2-pole breaker will disconnect neutral and hot at the same time, no matter the polarity.
Of course, we should all be testing unknown outlets beforehand, but I may not be the only person connecting the bus.